I have a unit that will not run any self test, refused... it say management device and front panel as internal fault.
it also say connect batteries on the front panel which it is conencted.
would that be the unit or just the battery ?
thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:15 AM . Last Modified: 2024-03-07 03:19 AM
The unit will not run a self-test if it thinks the battery is missing.
If the unit is reporting an active "internal fault" alarm (as opposed to just reporting it as the reason for not performing a self-test), then there's probably an issue with the UPS hardware.
Otherwise you could try re-seating the battery connectors and checking the voltage on the battery with a DVM.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:15 AM . Last Modified: 2024-03-07 03:19 AM
The unit will not run a self-test if it thinks the battery is missing.
If the unit is reporting an active "internal fault" alarm (as opposed to just reporting it as the reason for not performing a self-test), then there's probably an issue with the UPS hardware.
Otherwise you could try re-seating the battery connectors and checking the voltage on the battery with a DVM.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.