Smart-UPS 1400, strange behaviour, what is going on?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 1400, strange behaviour, what is going on?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:02 PM . Last Modified: ‎2024-03-14 03:48 AM

0 Likes
1
568
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:02 PM . Last Modified: ‎2024-03-14 03:48 AM

Smart-UPS 1400, strange behaviour, what is going on?

Couple of issues I've noticed:

1) I installed a new battery a few weeks ago (old one was completely dead), just recently I ran the runtime calibration through the Powerchute software, load on the UPS at the time was about 34%. Much to my disappointment, it only lasted about 10 minutes before ending the runtime calibration, and now the Powerchute software says I only have 9 minutes of backup time, this is with a 36% load only! At 45% it's even worst: 6 minutes and the battery LEDs start flashing. I would have expected the runtime to be much better than this especially with brand new batteries. Why is this?

2) Second thing that caught my attention, after the UPS returned to mains power following the runtime calibration, it switched back and forth between AC and battery for a period of a few minutes. About 1-2 seconds on battery, then about 10 seconds on AC, and all over and over again, with the time on AC getting progressively longer until eventually it stayed on AC power. This behavior can be reproduced, if I unplug it and let it run on battery for a couple minutes and plug it back in, it will do the same thing. Is this normal behavior? Some kind of self test or something?

Thanks in advance for any help/insight regarding these two issues.

Message was edited by: TheMG

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 11:02 PM . Last Modified: ‎2024-03-14 03:48 AM

0 Likes
0
568
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:02 PM . Last Modified: ‎2024-03-14 03:48 AM

TheMG,

The battery constants give the battery status via their life expectancy. If the battery ages and is “exhausted”, the constant is overwritten. The management software calculates the runtime of the UPS with these constants.If the battery is now replaced, a self test must be done with the new batteries. Through it, the red battery replace indicator goes out and the battery constants should be reset to the standard settings. This does not occur in some cases. Therefore, the constants must be reset manually. Please call in the APC Customer Care Center at 1-800-800-4272 as they can walk you through the steps to adjust the battery constant manually.

Regarding the second issue, I recommend you to adjust the UPS sensitivity to Medium or Low and check if the same situation persists. Click here to know the sensitivity adjustment procedure.

I hope that this helps.

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 11:02 PM . Last Modified: ‎2024-03-14 03:48 AM

0 Likes
0
569
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:02 PM . Last Modified: ‎2024-03-14 03:48 AM

TheMG,

The battery constants give the battery status via their life expectancy. If the battery ages and is “exhausted”, the constant is overwritten. The management software calculates the runtime of the UPS with these constants.If the battery is now replaced, a self test must be done with the new batteries. Through it, the red battery replace indicator goes out and the battery constants should be reset to the standard settings. This does not occur in some cases. Therefore, the constants must be reset manually. Please call in the APC Customer Care Center at 1-800-800-4272 as they can walk you through the steps to adjust the battery constant manually.

Regarding the second issue, I recommend you to adjust the UPS sensitivity to Medium or Low and check if the same situation persists. Click here to know the sensitivity adjustment procedure.

I hope that this helps.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of