Hi all, looks like a helpful community here so hopefully you can help me out too 🙂
I've done some reading, apologies if this is old news but I couldn't find the exact same problem.
I been given a pre-loved 10-year old Smart-UPS 1400, missing the battery. I've just put in new a genuine RBC7 which appears fine.
I'm using apcupsd on linux, and through that the battery reports 100% charge, but zero runtime remaining. All battery LEDs are lit, but flashing - indicating insufficient runtime at current load, I believe.
If I disconnect the serial line and kill the mains, the battery will happily support a 30% load for about 30 minutes, so it appears to actually work. All this time though the battery LEDs are flashing madly empty at me and the unit beeps constantly. I read that this is actually a calibration method, but afterwards nothing was changed unfortunately.
With the serial line connected, the daemon shuts the machine down straight away, as it sees the zero runtime and panics!
If I self-test the unit it straight away reports battery empty on both the LEDs and via serial port, and takes a few hours to "charge".
I've tried apcupsd's EEPROM Runtime Calibration, but the UPS aborts it straight away, because it thinks there's not enough run time to calibrate the run time 😞
Please don't tell me I need to find a Windows box to run something magic on!
Thanks, Tim.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:34 PM . Last Modified: 2024-03-15 01:34 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:34 PM . Last Modified: 2024-03-15 01:34 AM
Many thanks for the tip - I've requested info on how to find one through an email Tech Support and will keep you posted.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:34 PM . Last Modified: 2024-03-15 01:35 AM
Tim,
Call into Tech Support and request a calibration key. The APCUPSD won't be as efficient as this calibration key and should solve the problem for you.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:34 PM . Last Modified: 2024-03-15 01:34 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:34 PM . Last Modified: 2024-03-15 01:34 AM
Many thanks for the tip - I've requested info on how to find one through an email Tech Support and will keep you posted.