Smart UPS shows auto self test fail but Battery status LED's are fully lit?
Warning bleeps for approx 1 minute are repeated regularly
Do I need to replace the batteries?
Thks
Posted: 2021-07-07 11:41 PM
This reply was originally posted by Cristian on APC forums on 10/31/2017
Hi Robin , yes you need to replace the batteries and check the charger , but dont forget that you or a schneider service need to calibrate the charger when you change the batteries in that model .