Smart-UPS 1400 RM XL external battery amp hours?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 1400 RM XL external battery amp hours?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:12 AM . Last Modified: ‎2024-03-12 03:14 AM

0 Likes
3
983
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:12 AM . Last Modified: ‎2024-03-12 03:14 AM

Smart-UPS 1400 RM XL external battery amp hours?

I have a Smart-UPS 1400 RM XL, I have removed the internal batteries and am running a pair of 77AH AGM batteries externally (in series for 24v.)

On the network card, there is a field for 'Number of External Batteries'

What is the AH rating of the APC external battery pack? ie: How many 'battery packs' should I tell the UPS that it has attached?

Also, when the UPS is showing the available (calculated) runtime (based on number of battery packs installed)...

is this calculated runtime used to shut down the UPS after a certain number minutes OR does the UPS run until a certain battery voltage is reached?

thanks

bill

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:12 AM . Last Modified: ‎2024-03-12 03:14 AM

0 Likes
0
983
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:12 AM . Last Modified: ‎2024-03-12 03:14 AM

Thanks! I was able to look up the UPS user's guide and found it supports SU24RMXLBP2U.

Now, if we look at that (http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SU24RMXLBP2U), it says:

Battery Volt-Amp-Hour Capacity - 864 - someone helped me to determine that 864VAH/24V = 36AH.

When I dug into the build instructions for the external battery pack SKU, just to double check, I see that the SKU actually has two battery strings in it and each string has qty (4) of BATTERY 12V 9AH. This is wired in parallel to give you a 12V 36AH battery string. So, seems as though 36AH per pack is accurate as there are two 12V strings wired in series to give you a 24V, 36AH battery pack.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:12 AM . Last Modified: ‎2024-03-12 03:14 AM

0 Likes
0
983
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:12 AM . Last Modified: ‎2024-03-12 03:14 AM

Hmm, I was thinking that UPS would use a 48V battery system...

I also found this which I was poking around in that also said 48V.. http://www.apcmedia.com/salestools/ASTE-6Z8L99/ASTE-6Z8L99_R0_EN.pdf

Can you confirm the exact SKU from the rear of the UPS? Once I confirm the correct battery pack, I can look further into the AH capacity of it.

As for what the user sees, the UPS will shutdown when it reaches a "low battery" which is a value in minutes. I think probably internally it also factors in that it shouldn't discharge the battery below a particular battery voltage though.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:12 AM . Last Modified: ‎2024-03-12 03:14 AM

0 Likes
0
983
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:12 AM . Last Modified: ‎2024-03-12 03:14 AM

SU1400RMXLB3U

I measured the voltage at the battery connector before connecting the batteries up, 27.6 volts.

thanks

bill

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:12 AM . Last Modified: ‎2024-03-12 03:14 AM

0 Likes
0
984
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:12 AM . Last Modified: ‎2024-03-12 03:14 AM

Thanks! I was able to look up the UPS user's guide and found it supports SU24RMXLBP2U.

Now, if we look at that (http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SU24RMXLBP2U), it says:

Battery Volt-Amp-Hour Capacity - 864 - someone helped me to determine that 864VAH/24V = 36AH.

When I dug into the build instructions for the external battery pack SKU, just to double check, I see that the SKU actually has two battery strings in it and each string has qty (4) of BATTERY 12V 9AH. This is wired in parallel to give you a 12V 36AH battery string. So, seems as though 36AH per pack is accurate as there are two 12V strings wired in series to give you a 24V, 36AH battery pack.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore