Smart-UPS 1000 XL - run time ....

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 1000 XL - run time ....
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:03 AM . Last Modified: ‎2024-03-13 12:05 AM

0 Likes
1
701
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:03 AM . Last Modified: ‎2024-03-13 12:05 AM

Smart-UPS 1000 XL - run time ....

I have a Smart-UPS 1000 XL with 4 battery packs chained off of it...

the management page reports

2.5 hours of run time

Load Power:6.5 %Watts
Apparent Load Power:6.5 %VA
Load Current:0.3 Amps

I have ran a run time calibration ... ,,, it took about  32 hours to complete,,, and still report 2.5 hours...

is 2.5 hours the actual runtime on battery ??? or is it 32 hours ?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:03 AM . Last Modified: ‎2024-03-13 12:05 AM

0 Likes
0
700
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:03 AM . Last Modified: ‎2024-03-13 12:05 AM

Based on this, it certainly seems like it should be reporting closer to the 32 hours -> http://www.apc.com/resource/include/ups_runtime_chart.cfm?base_sku=SUA1000XL&family_id=165

I think that for a calibration to work well on most units, the load needs to be at least 30% and not fluctuate +/- 5%. So, perhaps it did not update properly because your load is so low on this unit.

I understand you want the runtime to be accurate but if you do more calibrations, whether its manual or a software one with a higher load as I've described, this will cause unnecessary discharges of your batteries. If you do want to calibrate it again, I would not do it unless you can increase the load and if you did do it, I'd probably do it manually since you already tried the software one. Manually requires letting it run with no software attached until it completely turns off (which any load attached would then turn off). Then, you let it charge back up.

Alternatively, you could wait for it to go on battery itself and adjust its own runtime during power outages, knowing you should get about 32 hours.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:03 AM . Last Modified: ‎2024-03-13 12:05 AM

0 Likes
0
701
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:03 AM . Last Modified: ‎2024-03-13 12:05 AM

Based on this, it certainly seems like it should be reporting closer to the 32 hours -> http://www.apc.com/resource/include/ups_runtime_chart.cfm?base_sku=SUA1000XL&family_id=165

I think that for a calibration to work well on most units, the load needs to be at least 30% and not fluctuate +/- 5%. So, perhaps it did not update properly because your load is so low on this unit.

I understand you want the runtime to be accurate but if you do more calibrations, whether its manual or a software one with a higher load as I've described, this will cause unnecessary discharges of your batteries. If you do want to calibrate it again, I would not do it unless you can increase the load and if you did do it, I'd probably do it manually since you already tried the software one. Manually requires letting it run with no software attached until it completely turns off (which any load attached would then turn off). Then, you let it charge back up.

Alternatively, you could wait for it to go on battery itself and adjust its own runtime during power outages, knowing you should get about 32 hours.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.