Posted: 2021-07-01 05:10 AM . Last Modified: 2024-03-05 01:42 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:10 AM . Last Modified: 2024-03-05 01:42 AM
Hi,
We install Powerchute using an MDT silent installation. This has always worked perfectly until we upgraded to Powerchute 3.1. Since doing so the silent installer on longer works. Although we specify REGISTER_WITH_NMC=no (as we cannot automate the registration) in the SilentIntsaller.ini it insists on trying to register and then complains about Mode not being valid. This was never a problem with 3.0. Does anyone know how to fix this?
Many thanks,
Rob
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:10 AM . Last Modified: 2024-03-05 01:42 AM
It is possible SilentInstaller.ini is corrupt. Can you get a new copy of it from a new download of the .exe or from an existing installation of PowerChute Network Shutdown on a different system?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:10 AM . Last Modified: 2024-03-05 01:42 AM
It is possible SilentInstaller.ini is corrupt. Can you get a new copy of it from a new download of the .exe or from an existing installation of PowerChute Network Shutdown on a different system?