hello,
We would like to test our new enviremont without draining the battery.
Regards
Stijn
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:10 AM . Last Modified: 2024-03-05 01:42 AM
Hi,
You can test PCNS with the NMC by going to Control on the NMC and selecting one of these Reboot, Turn UPS Off, Put UPS to Sleep, Put in Bypass and then click on Signal PowerChute Network Shutdown Clients.
You will then see this screen that describes how shutdown is configured.
The shutdown settings are can be found under the UPS tab - Configure - Shutdown.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:10 AM . Last Modified: 2024-03-05 01:42 AM
Hi,
What UPS do you have and what is the configuration? Have you installed PowerChute and if so what version?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:10 AM . Last Modified: 2024-03-05 01:42 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:10 AM . Last Modified: 2024-03-05 01:42 AM
Hi Bill,
We have a Symmetra 160K: SYMM_PX2 system.
We have configured PCNS 3.1 for vmware and some standolane clients (windows / linux) on fysical machines.
All the clients are configured with a shutdown delay if the UPS is a certain minutes on battery.
Some clients are PCNS 3.0
Regards and thanks in advance
Stijn
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:10 AM . Last Modified: 2024-03-05 01:42 AM
Hi,
You can test PCNS with the NMC by going to Control on the NMC and selecting one of these Reboot, Turn UPS Off, Put UPS to Sleep, Put in Bypass and then click on Signal PowerChute Network Shutdown Clients.
You will then see this screen that describes how shutdown is configured.
The shutdown settings are can be found under the UPS tab - Configure - Shutdown.