Dear All,
I have a cutomer whose Silcon 40kVA UPS was reportedly not coming out of automatic bypass. On visiting the customer, & seeing overload conditions reported in the log, I sent the UPS to manual bypass & shutdown the UPS. From there I did a systematic total power on procedure ( Step 1 -Q001 ON; Step 2 -Start Charging DC Capacitors; Step 3 - Closing of MCB - Capacitor Voltages shown to be 410 V on panel byth is time; Step 4 - Power ON). UPS goes initially to a normal operation, but shows the load as 158%. After about 20 seconds the UPS goes to automatic Bypass. On observing the Error log thereafter the relevant parts as follows:
Synchronization Error
Inverter Current Limiter Active
Overload-Load is over 100%
Battery MCB is off
Q003 on
Q002 off
.
.
What could be the problem ? If it is TSM related, which part or board of the TSM is faulty, since I am constrained with spares as well.
Thanking in advance,
Naleendra
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 04:47 AM . Last Modified: 2024-03-19 01:24 AM
If there really isn't an actual overload you should call into your local APC Customer Service office for tech support/Service Dispatch. There are to many variables that could be the issue with this unit.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 04:47 AM . Last Modified: 2024-03-19 01:24 AM
If there really isn't an actual overload you should call into your local APC Customer Service office for tech support/Service Dispatch. There are to many variables that could be the issue with this unit.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.