Shutting down ESXI and physical windows servers using PCNS using network and not power outlets

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Shutting down ESXI and physical windows servers using PCNS using network and not power outlets
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 01:02 AM . Last Modified: ‎2024-02-29 10:56 PM

0 Likes
3
1014
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:02 AM . Last Modified: ‎2024-02-29 10:56 PM

Shutting down ESXI and physical windows servers using PCNS using network and not power outlets

Hello

I have just purchased an SMT750RM2U UPS and am looking to use it to setup a controlled shutdown of my servers.

The UPS is plugged into the building MAINS, no servers are plugged into the UPS power outlets.

All the devices and servers are plugged into the building UPS, which lasts for about an hour.

I want to setup the Powerchute Network Shutdown and Powerchute Network Management Card software so that when the building mains power is lost, the UPS goes onto battery (runtime is over 4 hours as i have nothing plugged into it).

I want to run on battery for 30 minutes before starting a controlled shutdown of my physical windows servers and physical ESXI 5.5 hosts running VCentre server and 20 virtual windows machines.

I have installed the PCNS and PCMC software but am confused over the conflicting options on which should be configured first.

Also, if i want to shutdown physical machines via the network, do i need to install PCNS full software on each and every machine or is there a small agent that is installed that cannot control PCNS servers?

Thanks in advance

 

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:02 AM . Last Modified: ‎2024-02-29 10:56 PM

0 Likes
0
1013
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:02 AM . Last Modified: ‎2024-02-29 10:56 PM

Mark,

Yes. The hosts should be shut down. Review the PowerChute event log and in /opt/APC/PowerChute/group1 there is an error.log file that will list why the hosts were not shut down. In most cases it is caused be permissions but it can also be caused by a DNS issue.

If you see this error in the event log “Cannot connect to vCenter Server. PowerChute may not be able to issue commands to Virtual Machines or Hosts." then the issue is permissions. If you review the PowerChute Users Guide starting on page 110 of the PDF you will find errors and solutions.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:02 AM . Last Modified: ‎2024-02-29 10:56 PM

0 Likes
0
1013
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:02 AM . Last Modified: ‎2024-02-29 10:56 PM

Mark,

You should install PowerChute on each of the physical Windows server and configure them to power down the OS after UPS has been on battery for 30 minutes. To shutdown the ESXi host/s and VMs you can configure 1 of the physical Windows server to communicate with vCenter and shut down the host/s and VMs that way. Or you can install the PowerChute Appliance as a VM on a host and have it communicate with vCenter and the host/s for shut down.

Application Note 180 describes the option with VMware. You should review PowerChute Network Shutdown Standard Users Guide for help with the Windows setup. VMware Users Guides for help configuring for VMware. For help with the installation review PowerChute 4.0 Installation Guide.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 01:02 AM . Last Modified: ‎2024-02-29 10:56 PM

0 Likes
0
1013
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:02 AM . Last Modified: ‎2024-02-29 10:56 PM

Thanks Bill, much appreciated

I have also installed the software for the APC UPS Network Management Card, do the settings for this override any of the PCNS settings?

I have installed the PCNS on each physical windows machine and they shutdown perfectly.  I have also installed the PowerChute Appliance as a VM on one of the ESXi Hosts and it communicates with the hosts and i can shut them down fine, however, the ESXi hosts do not shutdown, but remain in Maintenance mode.

Is it possible to also shutdown the ESXi hosts?

I do not need any automated startup configured.

Many thanks

Mark 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:02 AM . Last Modified: ‎2024-02-29 10:56 PM

0 Likes
0
1014
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:02 AM . Last Modified: ‎2024-02-29 10:56 PM

Mark,

Yes. The hosts should be shut down. Review the PowerChute event log and in /opt/APC/PowerChute/group1 there is an error.log file that will list why the hosts were not shut down. In most cases it is caused be permissions but it can also be caused by a DNS issue.

If you see this error in the event log “Cannot connect to vCenter Server. PowerChute may not be able to issue commands to Virtual Machines or Hosts." then the issue is permissions. If you review the PowerChute Users Guide starting on page 110 of the PDF you will find errors and solutions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of