Shutdown if there is no WAN connection in external location

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Shutdown if there is no WAN connection in external location
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 12:27 AM . Last Modified: ‎2024-03-11 04:06 AM

0 Likes
9
1216
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:27 AM . Last Modified: ‎2024-03-11 04:06 AM

Shutdown if there is no WAN connection in external location

Hi all,

I tested a scenario:

we got a external location with a WAN connection, there is a Smart UPS 1500, and the automatic shutdown is performing well. with entering maintenance mode, migrate (if cluster), and shutting down AND no powering on(only manually)

all fine, but I think the trigger starts from the PCN appliance, isnt it? It doesnt matter if the config is already pushed on the APC in the location. Because in my scenario, I shut down the WAN Connection, so PCN Appliance (headquarter) got no communication with the APC (external, not Headquarter) but the switching in the external location between APC and Dell Server/ESX is established, though there is no trigger from APC 😕

I know this is the worst scenario ever, Power Problems and no WAN, but I hoped, the trigger is coming from the APC itself if there is no WAN communication with the pcn.

Anybody got an idea?

thanks in advance

danny

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:28 AM . Last Modified: ‎2024-03-11 04:06 AM

0 Likes
0
1216
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:28 AM . Last Modified: ‎2024-03-11 04:06 AM

Hi,

We offer a VM with PCNS preinstalled. You would deploy the VM on each host. See the PowerChute installation guide http://www.apc.com/salestools/PMAR-9HBK44/PMAR-9HBK44_R6_EN.pdf.

I also recommend you review the PowerChute User's guide http://www.apc.com/salestools/PMAR-9DNLQK/PMAR-9DNLQK_R3_EN.pdf?sdirect=true

If you are utilizing vCenter Server you should review Application Note 180 http://www.apc.com/salestools/SJHN-92FLU8/SJHN-92FLU8_R6_EN.pdf?sdirect=true

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:27 AM . Last Modified: ‎2024-03-11 04:06 AM

0 Likes
0
1216
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:27 AM . Last Modified: ‎2024-03-11 04:06 AM

Hi,

PowerChute Network Shutdown receives the UPS status over the network. You should have PCNS installed on the local ESXi host and that PCNS will communicate with the local UPS over the LAN. When the local UPS switches to battery the local PCNS will react and start the power down sequence for the local host/s.  

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 12:27 AM . Last Modified: ‎2024-03-11 04:06 AM

0 Likes
0
1216
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:27 AM . Last Modified: ‎2024-03-11 04:06 AM

Hi Bill,

like always thanks for the fast reply!

So this is the answer i thought so, that the PCNS triggers the communication.

PCNS on every ESXi? Is there an agent option? its not only 1 external locations, we got over 100 external locations on different places.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:28 AM . Last Modified: ‎2024-03-11 04:06 AM

0 Likes
0
1217
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:28 AM . Last Modified: ‎2024-03-11 04:06 AM

Hi,

We offer a VM with PCNS preinstalled. You would deploy the VM on each host. See the PowerChute installation guide http://www.apc.com/salestools/PMAR-9HBK44/PMAR-9HBK44_R6_EN.pdf.

I also recommend you review the PowerChute User's guide http://www.apc.com/salestools/PMAR-9DNLQK/PMAR-9DNLQK_R3_EN.pdf?sdirect=true

If you are utilizing vCenter Server you should review Application Note 180 http://www.apc.com/salestools/SJHN-92FLU8/SJHN-92FLU8_R6_EN.pdf?sdirect=true

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 12:28 AM . Last Modified: ‎2024-03-11 04:06 AM

0 Likes
0
1216
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:28 AM . Last Modified: ‎2024-03-11 04:06 AM

Hi Bill,

as always thanks for your fast replies... ok this can be a solution but not in our enviroment, because this are over 100 locations, and in this locations there are small enviroments with a few VMs, in this locations (external) we got VMware licensing by count of VMs.

so I see only one option, to install the Windows Solution on a running server where other services are installed too, without using another VM in any location.

Or maybe in my case it would be better to edit a network management card 2 User Config File, and upload this ini to every NMC 2 in the locations? With the NMC 2 ... is there a gently option to shutdown VMs too? Or is it only possible with PCNS?

Thanks a lot Bill

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:28 AM . Last Modified: ‎2024-03-11 04:06 AM

0 Likes
0
1216
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:28 AM . Last Modified: ‎2024-03-11 04:06 AM

Hi,

On 4/24/2018 4:22 AM, Danny said:

Or maybe in my case it would be better to edit a network management card 2 User Config File, and upload this ini to every NMC 2 in the locations? With the NMC 2 ... is there a gently option to shutdown VMs too?

Depending on the NMC there would be options to trigger a shutdown but the systems being shutdown would still need PowerChute installed on them. Smart-UPS SMT, SMX, SRT offer switched outlets and with a AP9630, or AP9631 installed would allow you to configure power down.

If you cannot install the PowerChute Appliance your other options are install PowerChute on VMware vMA or if that is not available as you mentioned install on a Windows system. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 12:28 AM . Last Modified: ‎2024-03-11 04:06 AM

0 Likes
0
1216
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:28 AM . Last Modified: ‎2024-03-11 04:06 AM

Hi Bill,

yes we got a Smart UPS 1500 DLT1500I and an AP9630 NMC, so is there a way to shutdown gently (Shutdown VMs, then Maintenance, then Power off?) without having Powerchute, or do you always need Powerchute for this?

thanks a lot.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:28 AM . Last Modified: ‎2024-03-11 04:05 AM

0 Likes
0
1216
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:28 AM . Last Modified: ‎2024-03-11 04:05 AM

Hi,

You will always need software on the computer to receive the signal from the NMC and to react to the signal. Example: install PCNS on Windows Server and configure it to listen to AP9630 install in Smart-UPS. The Smart-UPS switches to battery operation and the NMC sends a signal to PCNS. PCNS has been configured to start the shutdown process after the UPS has been on battery for 2 minutes. After waiting 2 minutes since no on line  message has been received PCNS starts the shutdown process. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 12:28 AM . Last Modified: ‎2024-03-11 04:05 AM

0 Likes
0
1216
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:28 AM . Last Modified: ‎2024-03-11 04:05 AM

ahh ok bill thanks a lot, then I did it right, I hoped there is a solution, that the networkmanagement card 2 (AP9630) has an extra option by it self, because of this many functions it brings with.

ok then I think about installing PCNS on a running Windows Server in the locations.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 12:28 AM . Last Modified: ‎2024-03-11 04:05 AM

0 Likes
0
1216
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:28 AM . Last Modified: ‎2024-03-11 04:05 AM

The network management card can shut down the UPS on its own (look into "Load Shedding" settings on the outlet groups) however like Bill said, your servers need software to tell them to safely shut down. PCNS is APC's solution; there are also third party tools: APCUPSd and NUT.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore