Shutdown delay

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Shutdown delay
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 08:36 AM . Last Modified: ‎2024-03-07 02:44 AM

0 Likes
7
2514
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:36 AM . Last Modified: ‎2024-03-07 02:44 AM

Shutdown delay

I have a BACK-UPS HT 1500. This unit is marketed for home theater but it has all the PC features, USB connection, etc, and I got a good deal on it so grabbed it.

PCPE sees it fine and is fully functional, but I'm finding that it doesn't appear to allow me to specify the time between initiation of system shutdown and when it cuts the UPS power, it isn't leaving enough time to shut down my OS as I have several things that happen prior to shutdown.

PCBE identifies it properly during install, but cannot see it after install, just says unknown device or whatever in the web GUI (windows sees it fine in device manager).

Is there a way to increase the shutdown delay in PE or get this working with BE?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 08:37 AM . Last Modified: ‎2024-03-07 02:44 AM

0 Likes
0
2515
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:37 AM . Last Modified: ‎2024-03-07 02:44 AM

Thanks. Just seems odd that it detects it fine during setup. The docs for PCBE say "virtually all USB UPSs" or something to that effect. My older smart-ups works fine with it so that confirms what you're saying.

Unfortunately no matter which option I choose (shut down after xx minutes or when xx minutes are left) it still uses the default delay of 1 or 2 minutes, which just isn't long enough for my OS to shut down.

I've switched back to native Windows 2008 support which does not signal the UPS to shut down after the PC is off, so I've set it to shut down when only 5% battery is remaining, and that seems to only leave a few minutes until the battery dies (I have a couple hundred watts of network equipment that doesn't require graceful shutdown and finishes off the battery) and the UPS shuts off, that'll have to be good enough for now.


JonPro wrote:
Hello DL, welcome to APC Forums.

PowerChute Personal Edition is the software designed to work with your current UPS. The PCBE software is designed to work with higher level UPS such as the APC Smart-UPS though there are Back-UPS that works with this software but all of them were already obsolete. One of the reason why it shows unknown device on the web interface is because of the method of communication and data exchange between the software and the UPS.

Unfortunately the solution that you can use to configure graceful shutdown is either the PCPE or the Native UPS software that comes along with your OS if your using Windows or Mac. On PCPE you can choose to shutdown your computer after running on a certain amount of time or when you only have a little amount of time left, if your computer takes time to shutdown you might need to choose the first one.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Anonymous user
Not applicable

Posted: ‎2021-06-30 08:36 AM . Last Modified: ‎2024-03-07 02:44 AM

0 Likes
0
2513
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:36 AM . Last Modified: ‎2024-03-07 02:44 AM

I have a BACK-UPS HT 1500. This unit is marketed for home theater but it has all the PC features, USB connection, etc, and I got a good deal on it so grabbed it.

PCPE sees it fine and is fully functional, but I'm finding that it doesn't appear to allow me to specify the time between initiation of system shutdown and when it cuts the UPS power, it isn't leaving enough time to shut down my OS as I have several things that happen prior to shutdown.

PCBE identifies it properly during install, but cannot see it after install, just says unknown device or whatever in the web GUI (windows sees it fine in device manager).

Is there a way to increase the shutdown delay in PE or get this working with BE?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:36 AM . Last Modified: ‎2024-03-07 02:44 AM

0 Likes
0
2513
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:36 AM . Last Modified: ‎2024-03-07 02:44 AM

here is the shutdown timeline for with and without PCPE:

Shutdown time line, software not installed:

1. UPS goes to battery, the on battery beep sounds
2. The UPS will sound the on battery beep until it reaches the last few minutes of run time. The length of time depends on the load and how old the battery is.
3. When the unit reaches the last few muntes of battery life it will then sound its low battery alarm.
4. Just before the battery is completely exhausted the ups will turn itself off.
5. If the UPS went to battery due to a brown out the unit at this point will be in LVSM until the voltage becomes acceptable again.

PowerChute Personal Edition default shutdown time line:

1. UPS goes to battery and PCPE starts its preserve battery power counter.
2. When the counter expires it sends a command to the UPS to start counting its turn off delay and then commands the OS to shutdown.
3. The operating system shuts down and the UPS continues to count its turn off delay. (Once the UPS finishes counting its turn off delay it will reboot and nothing can stop this from happening.)
4. The UPS cuts power to the outlets then rechecks to see if the incoming power is acceptable. If it is not it waits there until power returns.
5. If the UPS went to battery due to a brown out the unit at this point will be in LVSM until the voltage becomes acceptable again.


with PCBE, you get minimal (simple) support. you can only shutdown the computer based on a low battery signal (when the UPS has a low battery). there are no delays configurable within it that I can see, except for a command file that you can run for when the computer shuts down, based on that low battery signal. it is stated in the software here:

All events that have the shutdown action enabled will use the settings defined here. The shutdown sequence is as follows:
Execute a user-defined command file to perform custom actions such as a database shutdown (if enabled)
Begin the OS Shutdown after the Command File Execution Duration has expired
Turn the UPS off after the OS Shutdown Delay time has expired

the interface will look similar to my attachment and you only get to see if the UPS is "online" or "on battery." the only way to really test it is to pull the plug on the UPS and refresh the page.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:37 AM . Last Modified: ‎2024-03-07 02:44 AM

0 Likes
0
2513
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:37 AM . Last Modified: ‎2024-03-07 02:44 AM

you're right, the outlets on the UPS need to reboot before the UPS turns back on, cause if it doesnt, it doesnt know when to turn back on.

also, unfortunately, there is no way to tweak the delay in powerchute personal edition.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 08:37 AM . Last Modified: ‎2024-03-07 02:44 AM

0 Likes
0
2513
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:37 AM . Last Modified: ‎2024-03-07 02:44 AM

Hm, BE won't see it even in simple signalling. Which is odd because it detects and communicates with it fine during setup.

From what I can see, PE has a hard set timer of 1 or 2 mins depending on UPS model. Neither is sufficent for me. I guess I'll have to figure out what I'm going to do.

The built in support in Win 2008 works fine but the problem is, if the power comes back on before the UPS shuts itself off, the PC will never turn itself back on since the UPS won't know to reboot itself/bounce the ports, and that's the only way the PC knows to come back on. I guess as long as I set it to shut down when theres only a few % left and the possibility of that would be fairly minimal, just don't like cutting it that close on shutdown.

There is no hidden tweak to increase this 1 or 2 minute timer in PE?

Thanks for the info.

Message was edited by: drinkingbird

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 08:37 AM . Last Modified: ‎2024-03-07 02:44 AM

0 Likes
0
2513
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:37 AM . Last Modified: ‎2024-03-07 02:44 AM

I guess the only question left is should I be able to get this working with BE? It detects it automatically during install and doesn't report any errors, but after it is just "unknown device" in the web GUI. Same result when I select "simple signaling to any APC UPS" during setup.

From what I understand this is just a BACK-UPS RS with a different color case, but that isn't in the list of selections during setup. I guess I could try each one in the list but since that requires uninstall/reinstall each time it is a bit of a pain. I did try doing a hard reset on the UPS, shutting it down and holding the power button for 10 sec until all the lights lit up and shut off 1 by 1.

BE on the same PC can see my old Smart-UPS 1400 fine (connected via serial and USB to serial converter), unfortunately the batteries in that one are shot and this one offers much better runtime.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:37 AM . Last Modified: ‎2024-03-07 02:44 AM

0 Likes
0
2513
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:37 AM . Last Modified: ‎2024-03-07 02:44 AM

Hello DL, welcome to APC Forums.

PowerChute Personal Edition is the software designed to work with your current UPS. The PCBE software is designed to work with higher level UPS such as the APC Smart-UPS though there are Back-UPS that works with this software but all of them were already obsolete. One of the reason why it shows unknown device on the web interface is because of the method of communication and data exchange between the software and the UPS.

Unfortunately the solution that you can use to configure graceful shutdown is either the PCPE or the Native UPS software that comes along with your OS if your using Windows or Mac. On PCPE you can choose to shutdown your computer after running on a certain amount of time or when you only have a little amount of time left, if your computer takes time to shutdown you might need to choose the first one.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 08:37 AM . Last Modified: ‎2024-03-07 02:44 AM

0 Likes
0
2516
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:37 AM . Last Modified: ‎2024-03-07 02:44 AM

Thanks. Just seems odd that it detects it fine during setup. The docs for PCBE say "virtually all USB UPSs" or something to that effect. My older smart-ups works fine with it so that confirms what you're saying.

Unfortunately no matter which option I choose (shut down after xx minutes or when xx minutes are left) it still uses the default delay of 1 or 2 minutes, which just isn't long enough for my OS to shut down.

I've switched back to native Windows 2008 support which does not signal the UPS to shut down after the PC is off, so I've set it to shut down when only 5% battery is remaining, and that seems to only leave a few minutes until the battery dies (I have a couple hundred watts of network equipment that doesn't require graceful shutdown and finishes off the battery) and the UPS shuts off, that'll have to be good enough for now.


JonPro wrote:
Hello DL, welcome to APC Forums.

PowerChute Personal Edition is the software designed to work with your current UPS. The PCBE software is designed to work with higher level UPS such as the APC Smart-UPS though there are Back-UPS that works with this software but all of them were already obsolete. One of the reason why it shows unknown device on the web interface is because of the method of communication and data exchange between the software and the UPS.

Unfortunately the solution that you can use to configure graceful shutdown is either the PCPE or the Native UPS software that comes along with your OS if your using Windows or Mac. On PCPE you can choose to shutdown your computer after running on a certain amount of time or when you only have a little amount of time left, if your computer takes time to shutdown you might need to choose the first one.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore