Set battery install date
  • Set battery install date
cfoarfa
cfoarfa
Cadet
Posted: ‎2025-06-01 10:20 PM
497
I have an SMT750IC, connected via cable to the APC cloud ( website). How i can set the battery install date after replacement directly from the web interface or from the front device menu.
Thank you in advance
Kirk
Posted: ‎2025-06-02 05:40 AM
467
You may update the battery installation date if the system is connected to a computer running Power Chute Software (PCSS / PCBE).
Another option is to disconnect the battery connector and wait for the system to declare a battery fault.
Wait another ten seconds than reconnect the battery cable.
The system will prompt you to confirm if this is a new battery cartridge toggle from No to Yes. Enter the month & year and select enter.
Follow up by manually initiating a Self Test and let pass and allow the battery to recover to 100% SOC.
Complete the process by manually initiation a Battery Calibration with at least 30% attached load. Allow the procedure to complete and battery return to 100% SOC.
The above procedure will insure the operational runtime is displayed and seen is accurate as possible.
Questions Ask . . . 👍
cfoarfa
cfoarfa
Cadet
Posted: ‎2025-06-02 08:26 AM
In response to Teken
I will try the second recommendation