Server startup after power returns to UPS

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Server startup after power returns to UPS
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:23 PM . Last Modified: ‎2024-03-15 02:47 AM

0 Likes
10
5105
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:23 PM . Last Modified: ‎2024-03-15 02:47 AM

Server startup after power returns to UPS

We have a Smart-UPS 1500 RM with the network management card and two Apple Xserves connected to it.

The Xserves are running the PCNS software.

The runtime is about 40 minutes, and PCNS on the Xserves shuts the servers down after the "On-Battery" condition has lasted for 15 minutes.

After the Xserves have shut down, the UPS continues on battery power until the battery is drained. PCNS is not configured to shut down the UPS after the Xserve is shut down.

The Xserves are configured to restart after a power failure.

My problem is that when power is restored to the UPS after the Xserves have shut down, but while the UPS is still on battery power, the Xserves do not boot up again. Question 1: What can I do to ensure that the Xserves start up when power is restored to a UPS on battery power?

I'm not sure what happens if power is restored to the UPS after the battery has been drained and the UPS has turned itself off, as I haven't tested that yet. Question 2: Should the Xserves start up when power is restored to a UPS that has turned itself off?

I've read these two threads, but I'm not sure if the information applies to our setup:

https://community.se.com/t5/APC-UPS-Data-Center-Enterprise/bd-p/datacenter-forum

https://community.se.com/t5/EcoStruxure-IT-forum/bd-p/ecostruxure-it-forum

Thanks for any help.

Audun

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

0 Likes
0
5106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

>
so after reading that, the only issue you may run into is if the ups goes to battery, and the server shuts down and then the power is restored. the server will already have been shutdown but the UPS hasnt rebooted. in this case, you will need to manually restart the server.
Yes, that's what happened in my first test. I was hoping that the UPS could reboot automatically when power returns, as it is suggested in one of the threads I linked to in my first post. But I guess that isn't possible with the model we have.

Message was edited by: audunr

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:23 PM . Last Modified: ‎2024-03-15 02:47 AM

0 Likes
0
5106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:23 PM . Last Modified: ‎2024-03-15 02:47 AM

{quote:title=The Notorious K.M.P. wrote:}{quote}\r\n> Answer 2: If the UPS is off, power is cutoff, therefore the XServe cannot power itself up.\r\n\r\nAnd it won't power up again when power is returned to the UPS after it has turned itself off because the battery has been drained?

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 08:23 PM . Last Modified: ‎2024-03-15 02:47 AM

0 Likes
0
5106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:23 PM . Last Modified: ‎2024-03-15 02:47 AM

audunr wrote:Question 1: What can I do to ensure that the Xserves start up when power is restored to a UPS on battery power?
Question 2: Should the Xserves start up when power is restored to a UPS that has turned itself off?>

Answer 1: You would need to implement something like a switched rack PDU that would give you remote control to toggle power to the outlet that is powering the X serve.

Answer 2: If the UPS is off, power is cutoff, therefore the XServe cannot power itself up.

Reply

Link copied. Please paste this link to share this article on your social media post.

EZ_Button_apc
Commander EZ_Button_apc
Commander

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

0 Likes
0
5106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

If you just let the battery drain all the way down, the UPS will obviously shut off. When power is restored, the UPS will begin to charge, but will not turn on to provide power.

You will need to configure PCNS to turn off the UPS after the shutdown finnishes. This will put the UPS into sleep mode, which will turn off power on the output of the UPSand then when power returns, it will wake up and provide power to your servers.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

0 Likes
0
5106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

Thank you both for your replies.

We have two Xserves running PCNS. Should I configure PCNS on both Xserves to turn off the UPS, or just one of them?

In the former case, my guess is that the UPS will turn off as soon as the first of the Xserves sends the turn off signal. Which could cause problems if the 2nd Xserve hasn't shut down before the UPS switches itself off.

The UPS has a setting called "Shutdown Delay" at 90 seconds, which I guess is the amount of time that the 2nd Xserve has to shut down after the 1st Xserve has given the turn off signal to the UPS.

In the latter case, I guess I could configure PCNS on one of the Xserves to shut down the Xserve after 10 minutes without giving the turn off signal to the UPS, and the other Xserve to shut down after 15 minutes and then give the turn off signal to the UPS.

But in both cases, because the servers have shut themselves down, they will not power up automatically in this setup? In other words, the "power on automatically after a power failure" setting of Mac OS X only applies if power is suddenly lost without a graceful shutdown?

Reply

Link copied. Please paste this link to share this article on your social media post.

Cap1_apc
Lt. Commander Cap1_apc
Lt. Commander

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

0 Likes
0
5106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

The UPS will wait for confirmation from all of it's clients before starting it's own shutdown process. This means it'll start shutting down after seeing your second server send a shutdown confirmation.

Shutdown delay is a built in timer for the UPS to wait after it receives a shutdown command...this is basically a safety net for your load.

It depends on the BIOS setting, but most likely (from what you've already said) your servers will power back up when the power returns. Power MUST first be cut to the servers for this to work, which means the UPS must complete its graceful shutdown.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

0 Likes
0
5106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

with no software nor a network management card, if the UPS shuts down due to a low battery (which is 2 minutes if batt power left), shouldnt it turn back on afterwards? the default setting for any UPS is "reboot on line return" unless someone has changed this via software or management card.

am i wrong on that? i tested a symmetra with no configured management card and no PCNS clients. it shutdown due to low battery and when the power was restored, it powered right back on, saying shutdown due to low battery, and turned the load back on.

shouldnt it be the same deal with this one? as long as the BIOS settings are correct, they should turn back on because the UPS should be providing power.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

0 Likes
0
5106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

it should be true with all of APC's UPSs..

its just the fact that the UPS is on battery power and the server shuts down. so the server is turned off but there is still battery power available so when the utility power comes back, the server never really sees a chance in the power because there was either battery or utility power. the UPS would have had to shutdown and come back on to produce a change in state to it's output.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

0 Likes
0
5106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

>
The UPS will wait for confirmation from all of it's clients before starting it's own shutdown process. This means it'll start shutting down after seeing your second server send a shutdown confirmation.
Thank you. That bit of information is very helpful.

It depends on the BIOS setting, but most likely (from what you've already said) your servers will power back up when the power returns. Power MUST first be cut to the servers for this to work, which means the UPS must complete its graceful shutdown.
I hope this means that the Xserves, when shut down by PCNS, are shut down in a "special way", which causes them to automatically boot up again once power is restored to the UPS after the UPS has shut down. Maybe some "help I was shut down because of power failure" flag is set by PCNS?

Thanks for all the help!

It seems that testing is, as always, necessary to find out if what you think will happen actually happens.

Message was edited by: audunr

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

0 Likes
0
5105
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

PCNS gracefully shuts down the machine. the BIOS needs to be set to last state for this machine to come back on after the UPS has been shutdown and restarted.

[refer to this link|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=1191]

so after reading that, the only issue you may run into is if the ups goes to battery, and the server shuts down and then the power is restored. the server will already have been shutdown but the UPS hasnt rebooted. in this case, you will need to manually restart the server.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

0 Likes
0
5107
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

>
so after reading that, the only issue you may run into is if the ups goes to battery, and the server shuts down and then the power is restored. the server will already have been shutdown but the UPS hasnt rebooted. in this case, you will need to manually restart the server.
Yes, that's what happened in my first test. I was hoping that the UPS could reboot automatically when power returns, as it is suggested in one of the threads I linked to in my first post. But I guess that isn't possible with the model we have.

Message was edited by: audunr

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of