2200XL additional Battery Pack

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • 2200XL additional Battery Pack
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

0 Likes
9
1693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

2200XL additional Battery Pack

Could anyone advise if it's possible to purchase additional battery packs for the APC 2200XL?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 2200xl
  • additional
  • battery
  • pack
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

0 Likes
0
1693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

For the SUA2200RMI2U/SUA2200RM2U, the internal battery is the RBC43:

http://www.apc.com/resource/include/techspec_index.cfm?base_sku=RBC43

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

0 Likes
0
1693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

Could anyone advise if it's possible to purchase additional battery packs for the APC 2200XL?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

0 Likes
0
1693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

I think the model number is Smart-UPS 2200 RM

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

0 Likes
0
1693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

Tracked down one of the 2200s we typically use. The model numbers on the back of the UPS are SUA2200RMI2U followed by YS0 3I6LL248 (it was hard to see if the I were either 1s, Is or Ls

thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

0 Likes
0
1693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

Can you provide what the model number is of the 2200XL Smart-UPS?

There are a few different ones available based on the model number of the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

0 Likes
0
1693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

Aled,

When obtaining the model number from the UPS through either Software or Remote interaction, it's going to generalize the family name, so it will tell you something like "Smart-UPS 2200 RM XL". However, in order to determine which battery packs are compatible with your UPS setup, we would need the full model number from the white barcoded sticker on the rear of the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

0 Likes
0
1693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

Hi Kevin,

Many thanks for the information very helpful and quick responses. It's useful to know that the internal batteries can be replaced even if additional batteries cannot be installed. The units we have are now approx 5 years old so the internal batteries are probably in need of replacing now and this could be a better way of spending our money rather than trying to upgrade every single unit to a bigger unit (we have around 30 of them).

We also have a handful of the SU2200RMXLINET units, are additional batteries supported on this unit?

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

0 Likes
0
1693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

Aled,

Looks like you can use the SU48RMXLBP:

http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SU48RMXLBP

That seems to be the only battery option for the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

0 Likes
0
1693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

Thanks again Kevin, excellent quick response.

It's good to finally find a forum where an honest and accurate answer is provided rather than a supplier insisting we would need to upgrade to x/y or z models.

Would you by chance know the link for the internal battery we would need to order?

Many thanks again.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

0 Likes
0
1694
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-15 02:46 AM

For the SUA2200RMI2U/SUA2200RM2U, the internal battery is the RBC43:

http://www.apc.com/resource/include/techspec_index.cfm?base_sku=RBC43

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore