Server restarts when switching to battery

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Server restarts when switching to battery
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: โ€Ž2021-06-30 04:48 AM . Last Modified: โ€Ž2024-03-08 04:04 AM

0 Likes
9
2125
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 04:48 AM . Last Modified: โ€Ž2024-03-08 04:04 AM

Server restarts when switching to battery

HI Folks,

I just purchased a 2nd hand UPS (Smart-UPS 1400VA 2U) with new batteries.

I have 4 servers connected to it. When I pull the utility power from the UPS, 3 of my servers are fine however the Dell Poweredge R200 restarts (as if the power isn't being flipped over quick enough..)

The other 2 servers are HP and the 1 other is a VIA EPIA firewall (They are fine).

I used to have another Smart-UPS 1400VA (but not the rack version) and it as fine..

Help is appreciated cheers.

P.S. I'm not using PowerChute

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: โ€Ž2021-06-30 04:49 AM . Last Modified: โ€Ž2024-03-08 04:03 AM

0 Likes
0
2124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 04:49 AM . Last Modified: โ€Ž2024-03-08 04:03 AM

I'm sorry I don't have a management card and I can't use powerchute as I don't have the APC serial cable.

I am using a surge protector daisy chained onto the UPS however disconnecting it still causes the problem.

The 2 HP servers and 1 Dell (problem) server is plugged directly into the UPS with the surge protect daisy chain being used for the firewall, switches, modems etc..

Where can I find the serial number of this unit?

Overall, using my power meter, the whole rack takes up about 360W.

What really gets me is that the HP servers seem happy as anything!

I havn't tried the Dell completly alone. I will do that in a couple of hours when I can take the rack down as it is being used currently.
With everything connected, 2 load LEDs light up

Message was edited by: jonnytabpni

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
Anonymous user
Not applicable

Posted: โ€Ž2021-06-30 04:49 AM . Last Modified: โ€Ž2024-03-08 04:04 AM

0 Likes
0
2124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 04:49 AM . Last Modified: โ€Ž2024-03-08 04:04 AM

Ok I narrowed it down a bit...

If you look at my post above, I have 2 HP servers. They are different models.

If I disconnect the ML310G5 HP server, the Dell stays on no problem. Even if I replace the ML310G5 with my desktop Core2 Quad Q6600 and pull the plug, the Dell stays on ok when the plug is pulled.

It's as if the PSU of the ML310G5 is interfearing with the Dell's ability to withstand the "flip-over to battery"...

Any ideas?

Cheers

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-30 04:49 AM . Last Modified: โ€Ž2024-03-08 04:04 AM

0 Likes
0
2124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 04:49 AM . Last Modified: โ€Ž2024-03-08 04:04 AM

Ok just trash my theory on the HP server causing problems.

Just seems to be the Dell having issues with this UPS...
Sometimes it stays on..sometimes it reboots...

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-30 04:49 AM . Last Modified: โ€Ž2024-03-08 04:03 AM

0 Likes
0
2124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 04:49 AM . Last Modified: โ€Ž2024-03-08 04:03 AM

one other thing that i will throw out there could be transfer time to and from battery.

regular Smart UPS (not SC or RT families) take about 2-4ms to transfer to battery. a lot of high end, sensitive equipment cant take this and may reboot or turn off. i cant say from experience that i see it a lot with Dell servers but i will just mention it. if it were the case, it may be require a UPS with 0ms transfer time, such as a Smart UPS RT.

but before we assume that, since I dont think it's the case, do you have another UPS to try this server with? also, does this server have redundant power supplies?

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: โ€Ž2021-06-30 04:49 AM . Last Modified: โ€Ž2024-03-08 04:03 AM

0 Likes
0
2124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 04:49 AM . Last Modified: โ€Ž2024-03-08 04:03 AM

jonnytabpni wrote:
Someone else suggested to me that due to the inital surge on the UPS when switching to battery, the waveform may be less that what the Dell server can handle. This is probably due to worn capacitors or something.

I'm waiting on an APC Line-R to see if that fixes the issue. I'm going to put it between the UPS and the Dell Server.
I don't think that's going to matter. There is no initial surge when transferring to battery, but there is that 2-4 ms blackout time. So it goes from AVR corrected input power to blackout to battery power (pure sine) in that period of time. If the Server works fine on another Smart-UPS, then I'd say the UPS is the problem, and it's probably just worn due to age. However, I don't see the Line-R doing anything for you since it's going to regulate the voltage, and if it's a "surge" as you've been told, the Line-R output is going to be 0VAC.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-30 04:49 AM . Last Modified: โ€Ž2024-03-08 04:03 AM

0 Likes
0
2124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 04:49 AM . Last Modified: โ€Ž2024-03-08 04:03 AM

Oh I forgot to mention that I tried the UPS with the only thing plugged in being the Dell and it's all fine...

I'm kinda hoping that the Line-R will add some extra capacitance just enough to let the Dell server hold out long enough.
I don't understand why the Dell server is the only one causing an issue when all the servers are on the UPS...

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-30 04:49 AM . Last Modified: โ€Ž2024-03-08 04:03 AM

0 Likes
0
2124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 04:49 AM . Last Modified: โ€Ž2024-03-08 04:03 AM

Thanks for your reply.

As noted above, I do have another APC UPS (Smart-UPS 1400VA non-rackmount) and the Dell Server is fine with it.

Someone else suggested to me that due to the inital surge on the UPS when switching to battery, the waveform may be less that what the Dell server can handle. This is probably due to worn capacitors or something.

I'm waiting on an APC Line-R to see if that fixes the issue. I'm going to put it between the UPS and the Dell Server.

I know APC don't reccomend daisy chaining surge protection devices however the Smart-UPS is a true Sine Wave machine so it shouldn't be anywhere near as bad as a stepped-approx'ed one.

Any comments?

Cheers ๐Ÿ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-30 04:49 AM . Last Modified: โ€Ž2024-03-08 04:03 AM

0 Likes
0
2124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 04:49 AM . Last Modified: โ€Ž2024-03-08 04:03 AM

how many load LEDs are lit up on the UPS with everything connected?

just for the heck of it, did you try the Dell server COMPLETELY alone - I noticed you tried it with your desktop and one of the other servers...

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: โ€Ž2021-06-30 04:49 AM . Last Modified: โ€Ž2024-03-08 04:03 AM

0 Likes
0
2124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 04:49 AM . Last Modified: โ€Ž2024-03-08 04:03 AM

Do you have a network management card free that you could install in the UPS? Or...could you install our PowerChute software with no shutdown options enabled just to check on some of the data and events?

Are you using any daisy chained extension cords, surge protectors, or other UPS-type products in your configuration?

Finally...I notice from your other posts that you are using mainly international units. What is the exact model # on this UPS and do you know the power specs on the servers you plugged in?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-30 04:49 AM . Last Modified: โ€Ž2024-03-08 04:03 AM

0 Likes
0
2125
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 04:49 AM . Last Modified: โ€Ž2024-03-08 04:03 AM

I'm sorry I don't have a management card and I can't use powerchute as I don't have the APC serial cable.

I am using a surge protector daisy chained onto the UPS however disconnecting it still causes the problem.

The 2 HP servers and 1 Dell (problem) server is plugged directly into the UPS with the surge protect daisy chain being used for the firewall, switches, modems etc..

Where can I find the serial number of this unit?

Overall, using my power meter, the whole rack takes up about 360W.

What really gets me is that the HP servers seem happy as anything!

I havn't tried the Dell completly alone. I will do that in a couple of hours when I can take the rack down as it is being used currently.
With everything connected, 2 load LEDs light up

Message was edited by: jonnytabpni

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of