Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Serial communication to APC Smart UPS SMX3000RMHV2U

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: Serial communication to APC Smart UPS SMX3000RMHV2U
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
5059
voidstar_apc
voidstar_apc
196
Teken
Teken
162
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
BillP Leader
Leader

Posted: ‎2021-07-07 10:23 PM . Last Modified: ‎2024-03-04 10:45 PM

0 Likes
4
10541
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:23 PM . Last Modified: ‎2024-03-04 10:45 PM

Serial communication to APC Smart UPS SMX3000RMHV2U

Hi,

I am trying to establish a serial communication to APC Smart UPS model : SMX3000RMHV2U by using the included serial cable. I used the following parameters from "Checking UPS Communications on Windows" manual: - Baudrate : 2400,8,N,1 I sent a "Y" character, the UPS returned nothing which according to the manual should respond with "SM" characters. Then I send another "A", again the UPS returned nothing. This UPS and cable are fresh out of box and I tested and can confirm that my serial port is working. Any idea what might be the issue here — settings and command wise? Thank you!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • serial
  • smx
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
BillP Leader
Leader

Posted: ‎2021-07-07 10:24 PM . Last Modified: ‎2024-03-04 10:45 PM

0 Likes
1
10535
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:24 PM . Last Modified: ‎2024-03-04 10:45 PM

Hi Angela,

You can ignore my previous message.

Eventhough I could not talk to the SMX UPS using serial connection directly, now I was able to measure pin 9 and 7 voltage of the electrical signals on the same serial port. When the UPS is running on battery, it produced +5V consistently through these pins. And when the UPS runs off main AC power, it produced -5V. This way, I can integrate the voltage measurement to the microcontroller to shutdown equipment.

Thank you again for the whitepapers!

--

Ed

See Answer In Context

  • Tags:
  • electrical-signal
  • smx
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
BillP Leader
Leader

Posted: ‎2021-07-07 10:23 PM . Last Modified: ‎2024-03-04 10:45 PM

0 Likes
0
10536
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:23 PM . Last Modified: ‎2024-03-04 10:45 PM

The way you're trying to talk to this UPS is only applicable to older models that begin with model prefix SU, SUA, SUM, SURT, SURTA and a few select others. You won't be able to talk directly to this UPS as it speaks a different language.

The following application notes may help you to understand the different options for different UPS models and how you may be able to communicate with them:

www.apc.com/whitepaper/?an=176 (these UPSs can talk Modbus which can be used for custom applications)

www.apc.com/whitepaper/?an=181 (outlines different communication options for Smart-UPS in general)

www.apc.com/whitepaper/?an=178 (covers USB HID implementation if USB is an option for you)

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-07-07 10:24 PM . Last Modified: ‎2024-03-04 10:45 PM

0 Likes
0
10536
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:24 PM . Last Modified: ‎2024-03-04 10:45 PM

Hi Angela,

Thank you for the whitepapers! I managed to drill down to document #18[1] which said it supports SMX model. What I am trying to do is quite simple — to connect a microcontroller to this SMX Smart-UPS and retrieve on battery / main power loss status, then proceed to shutdown the equipment if the UPS is on battery. The microcontroller I am using can be triggered through RS232 signal and a relay. But since this SMX Smart-UPS comes with a Serial port, I thought it might work interfacing it using it.

Coming back to document #18, specifically on page 7 and 8, it says something about Power Fail signal with Output Type 1 which indicates AC Power Failure. I think that is close to what I need. Do you have more info on this section?


[1] http://www.apcmedia.com/salestools/MPAO-9E5RB5/MPAO-9E5RB5_R1_EN.pdfnVL4u2WRpyJfcwZiAblhLQ%3D%3D.pngnVL4u2WRpyJfcwZiAblhLQ%3D%3D.png

Attachments
  • Tags:
  • smx
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-07-07 10:24 PM . Last Modified: ‎2024-03-04 10:45 PM

0 Likes
1
10536
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:24 PM . Last Modified: ‎2024-03-04 10:45 PM

Hi Angela,

You can ignore my previous message.

Eventhough I could not talk to the SMX UPS using serial connection directly, now I was able to measure pin 9 and 7 voltage of the electrical signals on the same serial port. When the UPS is running on battery, it produced +5V consistently through these pins. And when the UPS runs off main AC power, it produced -5V. This way, I can integrate the voltage measurement to the microcontroller to shutdown equipment.

Thank you again for the whitepapers!

--

Ed

  • Tags:
  • electrical-signal
  • smx
Reply

Link copied. Please paste this link to share this article on your social media post.

huyhuynh
huyhuynh
Explorer

Posted: ‎2022-02-03 03:04 PM

In response to BillP
0 Likes
0
10297
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-03 03:04 PM

Hi. I'm working on the exact same setup. I'm still trying to figure out how to check on the status of the UPS. I know we can use the serial that came with the UPS, Would you mind sharing with me your setup? I know you used a microcontroller to do so. I'm connecting the serial cable directly to my computer and use LabVIEW to see the states of the serial cable. However, the states don't seem to change at all when I unplug the UPS cable. I'd really appreciate it if you can share with me your setup. Thanks!

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.