Selftest failed - Smart UPS 5000 SUA5000RMI5U

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Selftest failed - Smart UPS 5000 SUA5000RMI5U
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:05 AM . Last Modified: ‎2024-03-18 02:48 AM

0 Likes
4
2080
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:05 AM . Last Modified: ‎2024-03-18 02:48 AM

Selftest failed - Smart UPS 5000 SUA5000RMI5U

One of our UPS's failed its scheduled selftest the other day, which was within the expected life expectancy of the batteries so we thought nothing of it and just replaced the batteries (RBC55) with a spare set we had on shelf for a while.

The new set of batteries didn't pass a selftest either so we figured they'd be on shelf too long (is that even possible?) and ordered a new set.

New set in place, waited for 100% charge (did seem to get there faster than the earlier spare set) and initiated a selftest - which failed yet again.

The displayed run time is within expectation, so other than the message that a failed battery exists, the device seems to be running fine.

Is there anything we can do at this point?

Logs:

14.05.2017     09:04:28     UPS: Failed a self-test.
14.05.2017     09:04:14     UPS: At least one faulty battery exists.
14.05.2017     09:04:11     UPS: A faulty battery no longer exists.
14.05.2017     09:04:11     UPS: Started a self-test.
10.05.2017     08:51:30     UPS: Failed a self-test.
10.05.2017     08:51:16     UPS: At least one faulty battery exists.
10.05.2017     08:51:14     UPS: Started a self-test.
10.05.2017     08:51:12     UPS: A faulty battery no longer exists.
05.05.2017     13:05:28     UPS: Failed a self-test.
05.05.2017     13:05:14     UPS: At least one faulty battery exists.
05.05.2017     13:05:12     UPS: Started a self-test.
05.05.2017     13:05:11     UPS: A faulty battery no longer exists.
05.05.2017     13:00:45     UPS: The battery is now installed.
05.05.2017     12:58:42     UPS: The battery is not installed properly.
03.05.2017     10:27:18     UPS: Failed a self-test.
03.05.2017     10:27:04     UPS: At least one faulty battery exists.
03.05.2017     10:27:02     UPS: Started a self-test.
03.05.2017     10:27:01     UPS: A faulty battery no longer exists.
01.05.2017     15:50:13     UPS: Failed a self-test.
01.05.2017     15:49:58     UPS: At least one faulty battery exists.
01.05.2017     15:49:56     UPS: Started a self-test.
01.05.2017     15:49:56     UPS: A faulty battery no longer exists.
01.05.2017     13:44:38     UPS: Failed a self-test.
01.05.2017     13:44:18     UPS: At least one faulty battery exists.
01.05.2017     13:44:16     UPS: A faulty battery no longer exists.
30.04.2017     09:05:44     UPS: Failed a self-test.
30.04.2017     09:05:30     UPS: At least one faulty battery exists.
30.04.2017     09:05:22     UPS: Started a self-test.
16.04.2017     09:06:48     UPS: Passed a self-test.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • battery
  • fault
  • selftest
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:05 AM . Last Modified: ‎2024-03-18 02:48 AM

0 Likes
0
2080
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:05 AM . Last Modified: ‎2024-03-18 02:48 AM

My personal suggestion would be to make sure you have left the new batteries (either set you purchased) in the UPS for at least 8-10 hours or overnight to charge (even if it says 100% sooner than that) and then run the self test and see if there is still an issue. I'd do this before you consider braindeading the UPS which I know is a huge inconvenience.

I don't know the ins and outs of how a battery works and its chemical make up but I know that the voltage can look good and the charge can be 100% but then you put a load on it and it can then ultimately be drained if it truly was not fully charged to start with. With what I suggested, it should help avoid giving you any false failed self tests once we know the batteries have charged and haven't had a load applied to them to drain them - which is what happens during a self test. The UPS is applying a load to the battery and measuring the voltage drop while comparing it to a stored table of expected values. If it is outside of that range for some reason, a replace battery alert will be flagged.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
MarkC_apc
Commander MarkC_apc
Commander

Posted: ‎2021-06-28 06:05 AM . Last Modified: ‎2024-03-18 02:48 AM

0 Likes
0
2080
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:05 AM . Last Modified: ‎2024-03-18 02:48 AM

If you have not tried "brain dead" restart - do a search on the forum and learn about this procedure to reset the "brain".  If it works to reset the battery fault, I'd then recommend then doing a battery recalibration procedure to make the run life more accurate.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:05 AM . Last Modified: ‎2024-03-18 02:48 AM

0 Likes
0
2080
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:05 AM . Last Modified: ‎2024-03-18 02:48 AM

I feared that had to be the next step.
It's going to fun planning that one; there's some important network equipment behind this UPS of which 'never' is a convenient time to power down.

Reply

Link copied. Please paste this link to share this article on your social media post.

MarkC_apc
Commander MarkC_apc
Commander

Posted: ‎2021-06-28 06:05 AM . Last Modified: ‎2024-03-18 02:48 AM

0 Likes
0
2080
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:05 AM . Last Modified: ‎2024-03-18 02:48 AM

I'll bet one of the knowledgeable APC techs can help with some ideas to "plan" rather than "react" to the eventual.  The only issue is $$$'s, but it's sort of pay me now or......

Good luck

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:05 AM . Last Modified: ‎2024-03-18 02:48 AM

0 Likes
0
2081
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:05 AM . Last Modified: ‎2024-03-18 02:48 AM

My personal suggestion would be to make sure you have left the new batteries (either set you purchased) in the UPS for at least 8-10 hours or overnight to charge (even if it says 100% sooner than that) and then run the self test and see if there is still an issue. I'd do this before you consider braindeading the UPS which I know is a huge inconvenience.

I don't know the ins and outs of how a battery works and its chemical make up but I know that the voltage can look good and the charge can be 100% but then you put a load on it and it can then ultimately be drained if it truly was not fully charged to start with. With what I suggested, it should help avoid giving you any false failed self tests once we know the batteries have charged and haven't had a load applied to them to drain them - which is what happens during a self test. The UPS is applying a load to the battery and measuring the voltage drop while comparing it to a stored table of expected values. If it is outside of that range for some reason, a replace battery alert will be flagged.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of