APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-18 12:56 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-18 12:56 AM
I get repeating error email notifications every 2 minutes from my Smart-UPS RT 15000 RM XL (message below)
" Critical - UPS: Self-Test Failed "
Logs:
02.12.2017 | 10:18:47 | Device | UPS: Self-Test Failed |
02.12.2017 | 10:17:59 | Device | UPS: Self-Test started. |
Did anybody have similar issue before?
Please, help!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-18 12:56 AM
Hi,
This means your UPS failed its battery self test. The batteries are likely bad and require replacement. This is what would be expected anywhere from 2-5 +years old depending on the battery usage, environment, etc.
If this UPS is new and/or in warranty, you'll want to contact technical support. Otherwise, it may just be time to purchase replacement batteries. A failed self test would normally try to warn you about 1 month ahead of when the UPS's batteries will fail completely. You'll definitely want to check into this ASAP - like age of your batteries, how many need to be replaced etc otherwise your UPS won't be able to support power outages if it is not resolved.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-18 12:56 AM
Hi,
This means your UPS failed its battery self test. The batteries are likely bad and require replacement. This is what would be expected anywhere from 2-5 +years old depending on the battery usage, environment, etc.
If this UPS is new and/or in warranty, you'll want to contact technical support. Otherwise, it may just be time to purchase replacement batteries. A failed self test would normally try to warn you about 1 month ahead of when the UPS's batteries will fail completely. You'll definitely want to check into this ASAP - like age of your batteries, how many need to be replaced etc otherwise your UPS won't be able to support power outages if it is not resolved.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.