Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Self-Test Depletes Battery Capacity Considerably on Smart-UPS RT 10000 XL

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Self-Test Depletes Battery Capacity Considerably on Smart-UPS RT 10000 XL
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:11 AM . Last Modified: ‎2024-03-07 03:26 AM

0 Likes
3
943
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:11 AM . Last Modified: ‎2024-03-07 03:26 AM

Self-Test Depletes Battery Capacity Considerably on Smart-UPS RT 10000 XL

We have two Smart-UPS RT 10000s, neither has any external battery packs installed:

UPS "A" Smart-UPS RT 10000 XL only has a 15% load and had two new RBC44/140s installed last October. A runtime calibration of this UPS was passed in March this year and resulted in 1 Hour 6 Minutes runtime. It was manufactured 23/6/05. But when a Self-Test is run on this UPS, it depletes the battery capacity to 61%.

UPS "B" Smart-UPS RT 10000 XL also had two new RBCs installed last September and has a greater load of 30%. Its runtime calibration was recently passed resulting in 30 minutes runtime. It was manufactured 20/6/08. Yet its Self-Test only depletes battery capacity to 90%, which is also consistent with the Self-Test results of the other 80 or so APC UPSs of various models that we operate.

So what would account for the huge drop in battery capacity when running the Self-Test on UPS "A"?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:11 AM . Last Modified: ‎2024-03-07 03:26 AM

0 Likes
0
944
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:11 AM . Last Modified: ‎2024-03-07 03:26 AM

Hi Liam

Just to let you know that during the process of resetting the calibration counter and then running a self-test, a faulty battery was identified. Replacing the batteries seems to have fixed the problem

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:11 AM . Last Modified: ‎2024-03-07 03:26 AM

0 Likes
0
944
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:11 AM . Last Modified: ‎2024-03-07 03:26 AM

Hi Roly - 

I would run another calibration on UPS "A", but I would first make sure that there is more than 30% load attached. I think the issue is likely related to calibration rather than a faulty battery issue. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:11 AM . Last Modified: ‎2024-03-07 03:26 AM

0 Likes
0
944
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:11 AM . Last Modified: ‎2024-03-07 03:26 AM

Hi Liam

Thanks for your reply. That's an interesting point, but I was under the impression from APC documentation that a UPS would refuse a calibration if there was not enough load present. In this case the calibration was allowed, so I assumed that the load was sufficient and hence that the resulting calibration was valid. Certainly it would be interesting to see what effect doubling its load would have.

However, the UPS is at a remote site some 50km away and given that its a 10kVA unit, doubling its load would present some practical problems.

I found a FAQ that suggests running a "Manual Runtime Calibration" in order to reset the microprocessor. http://www.apc.com/us/en/faqs/FA156538/ Option 3. But this would require downtime of the attached network equipment, so I'd rather not do that unless absolutely necessary.

I'm now also in discussion with APC Support about this issue so I will post back here when I have heard back from them.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:11 AM . Last Modified: ‎2024-03-07 03:26 AM

0 Likes
0
945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:11 AM . Last Modified: ‎2024-03-07 03:26 AM

Hi Liam

Just to let you know that during the process of resetting the calibration counter and then running a self-test, a faulty battery was identified. Replacing the batteries seems to have fixed the problem

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore