Seeking Compatible APC UPS for - Ubuntu Server / Dell Poweredge T310

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Seeking Compatible APC UPS for - Ubuntu Server / Dell Poweredge T310
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:02 AM . Last Modified: ‎2024-03-12 04:47 AM

0 Likes
1
1004
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:02 AM . Last Modified: ‎2024-03-12 04:47 AM

Seeking Compatible APC UPS for - Ubuntu Server / Dell Poweredge T310

I am seeking Compatible APC UPS for - Ubuntu Server / Dell Poweredge T310

Research indicates some newer APC smart UPS do not function with Linux APCUPSD .

I cannot find any confirmation of a current model that works will with linux. Please advise. 

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • backup
  • smartups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:03 AM . Last Modified: ‎2024-03-12 04:47 AM

0 Likes
0
1003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:03 AM . Last Modified: ‎2024-03-12 04:47 AM

I am on the apcupsd list and this announcement was recently sent:

Last week APC publicly released documentation[1] on a new UPS control and monitoring protocol, loosely referred to as MODBUS (after the historic industrial control protocol it is based on). The new protocol operates over RS232 serial lines as well as USB connections and is intended to supplement APC's proprietary Microlink protocol. Microlink is not going away, but APC has realized that third parties require access to UPS status and control information. Rather than publicly open Microlink, they have created another protocol to operate along side it.

APC provided early access to the MODBUS documentation as well as a test UPS, and over the last several months I have implemented MODBUS on apcupsd. Now that the protocol docs are public I have been able to commit the code changes to CVS and make this announcement. For now, apcupsd supports MODBUS over RS232 serial only. It DOES NOT support MODBUS over USB.

Many existing Microlink UPSes can be upgraded to support MODBUS via a firmware update. See [2]. Certain older models are not upgradeable. APC support will be your best contact for determining if your UPS supports a MODBUS upgrade the information linked below does not make it clear.

I will work to get a formal apcupsd release out in the coming weeks. Until then, feel free to pull the code from CVS (Branch-3_14) and build it locally. I'll also try to make a test build for Windows available soon.

--Adam

[1] <http://www.apc.com/whitepaper/?an=176>

[2] <How do I update the firmware of my SMT, SMX, or SMC series Smart-UPS? | FAQs | Schneider Electric IT...>

I also recently sent an email on the apcupsd mailing list with this:

Firmware with Modbus support is available for download now for tower Smart-UPS with model numbers starting with SMT running firmware version >= UPS 08.0 and all 2U rackmount Smart-UPS model numbers starting with SMT.  Visit How do I update the firmware of my SMT, SMX, or SMC series Smart-UPS? | FAQs | Schneider Electric IT... for details.

In order to update the firmware, the UPS output must be turned off, so it's more convenient to use a laptop than the UPS powered server itself to perform the update. At this time APC's Firmware Upgrade Wizard only runs under Windows, but we are investigating publishing a manual process which could be locally performed over a serial port connection by an advanced user with any operating system.  Modbus support for new Smart-UPS models is planned and the feasibility of back-porting to certain existing Smart-UPS models is under investigation.

So, USB connectivity has always been available for apcupsd and SMT/SMX UPS models. Serial connectivity was not available without the AP9620 Legacy Communications or now with the Modbus support we've implemented. Apparently, USB support for apcupsd and Modbus is not yet complete.

I'd look at the SMT models that have a firmware upgrade available if you'd like if you are going to use serial but USB has always been available. You just got a few less items than you used to on older UPS models via USB and apcupsd.

I hope that helps explain things!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:03 AM . Last Modified: ‎2024-03-12 04:47 AM

0 Likes
0
1004
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:03 AM . Last Modified: ‎2024-03-12 04:47 AM

I am on the apcupsd list and this announcement was recently sent:

Last week APC publicly released documentation[1] on a new UPS control and monitoring protocol, loosely referred to as MODBUS (after the historic industrial control protocol it is based on). The new protocol operates over RS232 serial lines as well as USB connections and is intended to supplement APC's proprietary Microlink protocol. Microlink is not going away, but APC has realized that third parties require access to UPS status and control information. Rather than publicly open Microlink, they have created another protocol to operate along side it.

APC provided early access to the MODBUS documentation as well as a test UPS, and over the last several months I have implemented MODBUS on apcupsd. Now that the protocol docs are public I have been able to commit the code changes to CVS and make this announcement. For now, apcupsd supports MODBUS over RS232 serial only. It DOES NOT support MODBUS over USB.

Many existing Microlink UPSes can be upgraded to support MODBUS via a firmware update. See [2]. Certain older models are not upgradeable. APC support will be your best contact for determining if your UPS supports a MODBUS upgrade the information linked below does not make it clear.

I will work to get a formal apcupsd release out in the coming weeks. Until then, feel free to pull the code from CVS (Branch-3_14) and build it locally. I'll also try to make a test build for Windows available soon.

--Adam

[1] <http://www.apc.com/whitepaper/?an=176>

[2] <How do I update the firmware of my SMT, SMX, or SMC series Smart-UPS? | FAQs | Schneider Electric IT...>

I also recently sent an email on the apcupsd mailing list with this:

Firmware with Modbus support is available for download now for tower Smart-UPS with model numbers starting with SMT running firmware version >= UPS 08.0 and all 2U rackmount Smart-UPS model numbers starting with SMT.  Visit How do I update the firmware of my SMT, SMX, or SMC series Smart-UPS? | FAQs | Schneider Electric IT... for details.

In order to update the firmware, the UPS output must be turned off, so it's more convenient to use a laptop than the UPS powered server itself to perform the update. At this time APC's Firmware Upgrade Wizard only runs under Windows, but we are investigating publishing a manual process which could be locally performed over a serial port connection by an advanced user with any operating system.  Modbus support for new Smart-UPS models is planned and the feasibility of back-porting to certain existing Smart-UPS models is under investigation.

So, USB connectivity has always been available for apcupsd and SMT/SMX UPS models. Serial connectivity was not available without the AP9620 Legacy Communications or now with the Modbus support we've implemented. Apparently, USB support for apcupsd and Modbus is not yet complete.

I'd look at the SMT models that have a firmware upgrade available if you'd like if you are going to use serial but USB has always been available. You just got a few less items than you used to on older UPS models via USB and apcupsd.

I hope that helps explain things!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.