Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Secure Connection Failed or 404 page not found. Cannot access UPS.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Secure Connection Failed or 404 page not found. Cannot access UPS.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
5059
voidstar_apc
voidstar_apc
196
Teken
Teken
164
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
parkcitygolfer
parkcitygolfer
Explorer

Posted: ‎2022-02-07 10:45 AM

0 Likes
4
8531
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-07 10:45 AM

Secure Connection Failed or 404 page not found. Cannot access UPS.

I have several of the Smart UPS-3000 models in 4 offices. I have one that all of a sudden is giving me these errors when i try to connect via web interface. I have googled this to death and tried all kinds of stuff. I just did a reset and no change. I also unseated the card and that didnt help either. It is pingable and I get cert errors like normal when accessing it but then it just fails. Ive tried on several browsers even old ones to see if it was a new SSL issue. Any help would be greatly appreciated. Thanks

Labels
  • Labels:
  • Business Power UPS
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
parkcitygolfer
parkcitygolfer
Explorer

Posted: ‎2022-02-07 11:44 AM

0 Likes
3
8506
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-07 11:44 AM

Thought i would update. I just did a full reset on the network card and started re configuring. I got about half way through and I was updating a page and it threw me out with a

Secure Connection Failed

An error occurred during a connection to xxx.xxx.xxx.xxx PR_CONNECT_RESET_ERROR

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2022-02-10 11:12 AM

In response to parkcitygolfer
0 Likes
2
8461
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-10 11:12 AM

@parkcitygolfer 

 

  1. What is the model of the network card and what firmware is it running? 
  2. Can you SSH or telnet to the card?
  3. Is the card local or are you connecting from a remote site?

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

parkcitygolfer
parkcitygolfer
Explorer

Posted: ‎2022-02-10 12:10 PM

In response to BillP
0 Likes
1
8456
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-10 12:10 PM

9631

Not sure of the firmware

Yes i can ssh to it. Telnet hits it too. I can also ping it. It will stay up for days if i dont make any changes but once i turn on NTP or change the name it instantly starts throwing that error.

Secure Connection Failed

An error occurred during a connection to 10.5.2.157. PR_CONNECT_RESET_ERROR

 

This is a local card on my network.

 

Thanks
Eric

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2022-02-18 01:24 PM

In response to parkcitygolfer
0 Likes
0
8444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-18 01:24 PM

@parkcitygolfer 

 

Logged into the card via FTP

  1. changed to the ssl directory
  2. del defaultcert.p15
  3. quit

Logged into the card via Telnet and reboot the card.

 

Once the card has rebooted upgrade the firmware to 7.0.4 

 

https://www.apc.com/shop/us/en/products/UPS-Network-Management-Card-v7-0-4-Firmware-for-Smart-UPS-Ga...

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.