I've had a symetric system working with the SYTF2 for around 9 months now (and I know it's been obsoleted but it did what it was supposed to do). Last night all the 120 VAC outlets stopped working. I checked the input line and it has power and have even opened up the unit to see if anything was smoked but it's pretty simple other than one large capacitor in the system. Is there anything else I could look at or is it likely that one capacitor is dead and I just need to replace it?
Mike
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:58 PM . Last Modified: 2024-03-14 03:51 AM
If you've confirmed that the 208v feed from the Symmetra is indeed measuring within range and the breaker on the back of the SYTF2 is in the ON position, and none of the push-breakers for the outlets are popped out, then I would confirm that the unit has failed. Purchasing a new unit would be your best option.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:58 PM . Last Modified: 2024-03-14 03:51 AM
If you've confirmed that the 208v feed from the Symmetra is indeed measuring within range and the breaker on the back of the SYTF2 is in the ON position, and none of the push-breakers for the outlets are popped out, then I would confirm that the unit has failed. Purchasing a new unit would be your best option.