Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

SYRXR4 Not Reporting Correct Battery Statistics Usage ?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SYRXR4 Not Reporting Correct Battery Statistics Usage ?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:12 AM . Last Modified: ‎2024-03-13 11:24 PM

0 Likes
0
501
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:12 AM . Last Modified: ‎2024-03-13 11:24 PM

SYRXR4 Not Reporting Correct Battery Statistics Usage ?

We have recently installed a Symmetra 6kva with the Extended Run Frame, and found that 4 out of 5 Extended run frames are not reporting the correct charge on the batteries.

When the SYRXR4 is connected with 4 brand new fully charged batteries installed, the Symetra front panel as well as the Power Chute web interface report battery charge at 57%. When we pull the same batteries out and place them into the chassis, and disconnect the XR4, it reports at 99% charge. Whiskey Tango Foxtrot over?

The display correctly reports the 7 batteries installed, and from the Power Chute interface, they all check in as "Good" ... It is only when the XR4 is connected that we are getting the wrong charge information. Any ideas?

Quality control on this order has been horrific. 6 out of 9 Symmetra 6kva chassis showed up with the back ends dented and the fan modules crushed in the exact same place as if they came off the production line this way. I can say this with a fair amount of certainty, as the APC boxes they are packed in are pristine, and everything is still in the plastic. 2 battery modules' pins broke off in the XR4 when attempting to remove them when the XR4 would not report the correct charge. Two other XR4s see the batteries, but will not report the charge ... and one of the Intelligence Modules pins had bent and broken pins coming right out of the packaging ... That factory in China manufacturing the AMERICAN Power Conversion components needs some oversight.

I am not feeling good about selecting APC over Liebert for this order. Hopefully the APC customer service makes up for the lack of quality control in their manufacturing.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • charge
  • incorrect
  • intelligence
  • symmetra
  • syrxr4
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of