SYMSTRF 1 (singlephase) no start-up / DEAD SET

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SYMSTRF 1 (singlephase) no start-up / DEAD SET
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:34 AM . Last Modified: ‎2024-03-12 11:22 PM

0 Likes
4
868
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:34 AM . Last Modified: ‎2024-03-12 11:22 PM

SYMSTRF 1 (singlephase) no start-up / DEAD SET

Hi forum.

We are having problems with a Symmetra Power Array Model SYMSTRF 1 (single phase model). After a period of non-operation we change all the batteries of

the unit and when we powered it up there was no Output from the UPS (no load present on the unit), no light indications present (no leds working on MIM nor RIM), screen or fans. No clicking/cycling sounds either. The whole unit is not powering up. DEAD SET.

I searched every manual i could find but the problem still remains. System enable switch is working / source input supply is ok

Please advice.

PS: I came across this conv. but the steps mentioned there didnt help me out and no final solution was mentioned.

SYMMETRA DEAD SET

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:34 AM . Last Modified: ‎2024-03-12 11:22 PM

0 Likes
0
868
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:34 AM . Last Modified: ‎2024-03-12 11:22 PM

There is no display when i remove the MIM / RIM and flip up the system enable switch.

I suspect the problem exists in the power supply of the auxiliary/secondary circuit (fans, display etc) on the RIM, MIM boards after a long period of non operation. That is way the drawings would be useful.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:34 AM . Last Modified: ‎2024-03-12 11:22 PM

0 Likes
0
868
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:34 AM . Last Modified: ‎2024-03-12 11:22 PM

Hi forum.

We are having problems with a Symmetra Power Array Model SYMSTRF 1 (single phase model). After a period of non-operation we change all the batteries of

the unit and when we powered it up there was no Output from the UPS (no load present on the unit), no light indications present (no leds working on MIM nor RIM), screen or fans. No clicking/cycling sounds either. The whole unit is not powering up. DEAD SET.

I searched every manual i could find but the problem still remains. System enable switch is working / source input supply is ok

Please advice.

PS: I came across this conv. but the steps mentioned there didnt help me out and no final solution was mentioned.

SYMMETRA DEAD SET

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:34 AM . Last Modified: ‎2024-03-12 11:22 PM

0 Likes
0
868
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:34 AM . Last Modified: ‎2024-03-12 11:22 PM

These older UPS should show signs of life as soon as the system enable switch on the rear is set to up and the input circuit breaker on the UPS is closed.  Even if the AC is not good, the batts being installed should be enough to at least get something assuming they are at a proper voltage.  What is the battery voltage?  These UPS use a 120 VDC nominal voltage but will float higher - around 137 VDC.

Do you get absolutely nothing on the screen or the intel modules?  How about if you close the maintenance bypass switch?  Does that give you any LEDs?  Any output power to the load if you check physically?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:34 AM . Last Modified: ‎2024-03-12 11:22 PM

0 Likes
0
870
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:34 AM . Last Modified: ‎2024-03-12 11:22 PM

First of all, thank you for your kind advice..

I am aware that the ups should show signs of life when the system enable switch is up and the input circuit breaker is closed however this is not happening (batts have been measured and tested ~ 125VDC).

There is no signal at all and no indication on the screen or intel modules. Not a single sound, or light/led even if we close the maintenance bypass switch. No output power at all.

Any ideas or directions would be appreciated.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:34 AM . Last Modified: ‎2024-03-12 11:22 PM

0 Likes
0
869
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:34 AM . Last Modified: ‎2024-03-12 11:22 PM

There is no display when i remove the MIM / RIM and flip up the system enable switch.

I suspect the problem exists in the power supply of the auxiliary/secondary circuit (fans, display etc) on the RIM, MIM boards after a long period of non operation. That is way the drawings would be useful.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of