This question was originally posted by MUHAMMAD on APC forums on 2/12/2019
Hi,
We have installed Symmetra PX-500 ups with NMC-AP9635CH. We are able to see alarms on UPS HMI and now need to integrate followings UPS alarms with BMS system on SNMP. I am using powernet426 MIB file. UPS Firmware detail is also attached for reference. Kindly share the OID for the following alarm/SNMP Points from Powernet 426 MIB file.
1) Loss of communication
2) Rectifier fuse blown alarm
3) Fan failure alarm
4) Inverter Non synchronous alarm
5) Abnormal voltage alarm
6) Abnormal frequency alarm
7) Input contactor fault alarm
😎 Module failure alarm
9) Bypass input power failure alarm
10) Loss of Local power
11) Battery fault
12) BCB tripped
Extension of external alarms showing Battery status