Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0806:08 AM. Last Modified: 2024-02-1512:06 AM
SYMMETRA PX 500 || SNMP Alarms on NMC-AP9635CH
Hi,
We have installed Symmetra PX-500 ups with NMC-AP9635CH. We are able to see alarms on UPS HMI and now need to integrate followings UPS alarms with BMS system on SNMP. I am using powernet426 MIB file. UPS Firmware detail is also attached for reference. Kindly share the OID for the following alarm/SNMP Points from Powernet 426 MIB file.
1) Loss of communication
2) Rectifier fuse blown alarm
3) Fan failure alarm
4) Inverter Non synchronous alarm
5) Abnormal voltage alarm
6) Abnormal frequency alarm
7) Input contactor fault alarm
😎 Module failure alarm
9) Bypass input power failure alarm
10) Loss of Local power
11) Battery fault
12) BCB tripped
Extension of external alarms showing Battery status