I have a number of these cards that work fine in a system but won't communicate over the DB9 Computer Interface port. I've set comms to 2400 baud, 8 data bit, no parity and no flow control. It used to work for me some years ago. Any magic? Perhaps that little jumper labeled J6? SYMIM rev lock? MIM is SYMIM2 FW: 112.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 11:50 PM . Last Modified: 2024-03-19 03:09 AM
Cable is a 940-0024C. Network card is pulled. This cable works with PX & LX systems.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 11:50 PM . Last Modified: 2024-03-19 03:09 AM
Hi Ken,
Are you using the cable provided with the unit--part number 940-0024? If you are trying to communicate with the Symmetra itself make sure the network card is pulled out--otherwise you will make a serial connection to the NMC.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 11:50 PM . Last Modified: 2024-03-19 03:09 AM
Cable is a 940-0024C. Network card is pulled. This cable works with PX & LX systems.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.