SUVT + MBP
  • SUVT + MBP
Posted: ‎2021-06-26 04:30 AM . Last Modified: ‎2024-03-19 01:27 AM
1259
SUVT + MBP
Hi everybody,
I have a question about the wiring between the MPB and the UPS.
I plugged the UPS control wire from the MBP (Pin 1 and Pin 2) to the J106 plug between Pin 5 (Q3 active) and Pin 6 (Q3 active return).
Is that right?
I just need to declare to the UPS that there's a MBP ("MPB Board On" on the UPS)
Thanks a lot
  • Data Center & Facility 3 Phase UPS
It's not the same MBP as mine...
http://www.apc.com/template/size/apc/sizing_display_options.cfm?option_type=SBP&ups_sku=SUVT10KH1B4S...
Samy
Replies 5
Hi Sam,
I've installed the MBP a couple of times.
Connect MBP X010 pin 1 & 2 to UPS J106 pin 5 & 6 respectively. Pin 1 & 2 is normally closed (shorted) when Q3 is in off position.
The UPS will assume MBP is present as long as pin 5 & 6 (J106) are closed (shorted). If you remove J106 terminal block UPS LCD will show:
UPS: The external Switch Gear Q003 has closed. and of course UPS will go into Maintenance Bypass.
Rgds, CHEE
Erasmus_apc
Sisko Erasmus_apc
Sisko
What style/model bypass switch do you have?
Reference is SBPSU10K20HC1M1-WP.
Thank you
Erasmus_apc
Sisko Erasmus_apc
Sisko
Alright. I would recommend calling in to our three-phase support team for immediate assistance. I'm a single phase guy so I end up going to them and posting a reply back here usually...
Their direct ph# is 877-287-7835.
Samy