SURTD3000RMXLT3U Discharged Battery, Runtime remaining 11 Sec's, Battery Capacity 100 %

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SURTD3000RMXLT3U Discharged Battery, Runtime remaining 11 Sec's, Battery Capacity 100 %
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:31 AM . Last Modified: ‎2024-03-12 11:27 PM

0 Likes
3
745
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:31 AM . Last Modified: ‎2024-03-12 11:27 PM

SURTD3000RMXLT3U Discharged Battery, Runtime remaining 11 Sec's, Battery Capacity 100 %

Hello,

Our Smart-UPS RT 3000 is having issues since we initiated a "Runtime Calibration". The UPS was fine beforehand.  It now states a runtime of 11 seconds with 100% battery capacity. The battery capicity lights are all lit but flashing. We unplugged the UPS and it held a 30% load for roughly 23 minutes so we don't beleive it to be a battery issue. How do we resolve this issue?

Model = Smart-UPS RT 3000 XL

Model number = SURTD30000RMXLT3U

Firmware = 5.1

Manu= 12-11-2010

Serial = IS1050009155

unit has SMART SLOT AP9630 Network Mgmt card

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:31 AM . Last Modified: ‎2024-03-12 11:26 PM

0 Likes
0
747
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:31 AM . Last Modified: ‎2024-03-12 11:26 PM

Hello Angela,

I did exactly as you suggested. The AP9630 card remains unseated, The UPS charging lights are steady and runtime capacity is incrementing upwards. I will re-seat the module once the charging has completed. Life is good, thank you. So is this a communications issue between the UPS and the Management Module?

Thanks Again,

JohnZ. smile


See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:31 AM . Last Modified: ‎2024-03-12 11:26 PM

0 Likes
0
747
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:31 AM . Last Modified: ‎2024-03-12 11:26 PM

Nope. It is a UPS calibration issue and we are removing the AP9630 just to make sure there is no configuration on it that could disrupt the calibration process (i.e. turn it off for some reason).

You're very welcome for the help.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:31 AM . Last Modified: ‎2024-03-12 11:27 PM

0 Likes
0
747
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:31 AM . Last Modified: ‎2024-03-12 11:27 PM

I think you might need to give it a go at another manual calibration. I would suggest, if possible, to go ahead and set it up so you can remove the AP9630 temporarily or unseat it. Then, you definitely need to make sure there is a minimum 30% load (which you mentioned) but it cannot fluctuate more than -/+ 5%. They key is in simulating the power failure by pulling the plug or tripping the upstream breaker to put the UPS on battery and you must let it run down to 0 and let it turn it off. Then, let it charge up afterwards again and check the runtime value. It is ok to re-install the AP9630 at this time as well and restore your normal load, understanding while it is charging if there is an outage, you won't have your full runtime available.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:31 AM . Last Modified: ‎2024-03-12 11:26 PM

0 Likes
0
748
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:31 AM . Last Modified: ‎2024-03-12 11:26 PM

Hello Angela,

I did exactly as you suggested. The AP9630 card remains unseated, The UPS charging lights are steady and runtime capacity is incrementing upwards. I will re-seat the module once the charging has completed. Life is good, thank you. So is this a communications issue between the UPS and the Management Module?

Thanks Again,

JohnZ. smile


Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:31 AM . Last Modified: ‎2024-03-12 11:26 PM

0 Likes
0
748
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:31 AM . Last Modified: ‎2024-03-12 11:26 PM

Nope. It is a UPS calibration issue and we are removing the AP9630 just to make sure there is no configuration on it that could disrupt the calibration process (i.e. turn it off for some reason).

You're very welcome for the help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of