SURTA3000XL - Power NM card without batteries ?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SURTA3000XL - Power NM card without batteries ?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 03:29 AM . Last Modified: ‎2024-03-18 04:37 AM

0 Likes
4
972
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:29 AM . Last Modified: ‎2024-03-18 04:37 AM

SURTA3000XL - Power NM card without batteries ?

Will a SURTA3000XL power the network mgt card or any other indicator lights without batteries? Trying to figure out if this used unit I just picked up is good or junk. I _assumed_, which I know is never good, that being an online unit w/ hotswappable batts, etc that it would pass power in the absence of the batteries but I've plugged it in and the NM card doesn't even power on & no output on any receptacle.

Bought w/ intention of grabbing new batts but don't wanna spend the cash without someway to test unit for DOA.

Thanks in advance for your educated input.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
mitsmith_apc
Lt. Commander mitsmith_apc
Lt. Commander

Posted: ‎2021-06-28 03:29 AM . Last Modified: ‎2024-03-18 04:37 AM

0 Likes
0
972
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:29 AM . Last Modified: ‎2024-03-18 04:37 AM

Hi Bill,

The unit will not power on without batteries so that is why there is no power to the output. As far as the NMC goes it will also not be powered if the capacitors inside the unit are not charged. Since the unit has been without batteries for a while I suspect that there is no charge in those capacitors and is thus why the NMC will not power on. At this point we would need some batteries to make any conclusion on the life of the unit.

-Mike

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
mitsmith_apc
Lt. Commander mitsmith_apc
Lt. Commander

Posted: ‎2021-06-28 03:29 AM . Last Modified: ‎2024-03-18 04:37 AM

0 Likes
0
973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:29 AM . Last Modified: ‎2024-03-18 04:37 AM

Hi Bill,

The unit will not power on without batteries so that is why there is no power to the output. As far as the NMC goes it will also not be powered if the capacitors inside the unit are not charged. Since the unit has been without batteries for a while I suspect that there is no charge in those capacitors and is thus why the NMC will not power on. At this point we would need some batteries to make any conclusion on the life of the unit.

-Mike

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 03:29 AM . Last Modified: ‎2024-03-18 04:37 AM

0 Likes
0
972
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:29 AM . Last Modified: ‎2024-03-18 04:37 AM

Thanks. That's what I needed to know. Will gamble & order some batteries.. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 03:29 AM . Last Modified: ‎2024-03-18 04:37 AM

0 Likes
0
972
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:29 AM . Last Modified: ‎2024-03-18 04:37 AM

Because it's so irritating when folks don't close the loop on forums, I wanted to check back in and confirm Mike's solution. I was able to source the batteries from Batteries Plus (Duracell) for around $260 and the unit sprang to life and checks out fine.

Thanks again, Mike!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:29 AM . Last Modified: ‎2024-03-18 04:37 AM

0 Likes
0
972
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:29 AM . Last Modified: ‎2024-03-18 04:37 AM

Hi Bill.  It appears that you don't mind using non-OEM batteries as I do.  For future reference, I just wanted to let you know that another company, Battery Sharks, has replacement batteries for your unit for about $140.

I've used them in the past and they have good deals on batteries especially if your UPS is out of warranty.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore