SURT3000XLI | Unable to access through hyper-terminal

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SURT3000XLI | Unable to access through hyper-terminal
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-27 11:14 PM . Last Modified: ‎2024-03-19 12:15 AM

0 Likes
6
2961
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:14 PM . Last Modified: ‎2024-03-19 12:15 AM

SURT3000XLI | Unable to access through hyper-terminal

Can someone please tell me if it's possible to reset the username and password on these devices. I am unable to access the device through hyper-terminal it's possible the previous keeper may have changed the default username and password. I am able to connect to the device through hyper-terminal but when I enter in the default username "apc" and password "apc" it just asks me for it again. After three attempts it tells me I'm locked out for 2 minutes.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 3000
  • apc
  • help
  • password
  • reset
  • surtd3000xli
  • ups
  • username
  • xli
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:14 PM . Last Modified: ‎2024-03-19 12:15 AM

0 Likes
0
2961
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:14 PM . Last Modified: ‎2024-03-19 12:15 AM

Hi,

The SURTD model Smart-UPS have limited access over serial communications.  

The SURTD models do not support UPSLink commands like the SUA model units do. 

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:14 PM . Last Modified: ‎2024-03-19 12:15 AM

0 Likes
0
2961
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:14 PM . Last Modified: ‎2024-03-19 12:15 AM

Hi

I have a SURTD3000XLi and the menu is reduced as shown in the photo. I need to modify the battery constant and I cannot access the hidden menu. I did it without problems in several UPS but in this I could not. The UPS also has a network board but I tried to remove it and it didn't work either. Does anyone know how to enter the hidden menu for these cases?

Thank you

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:14 PM . Last Modified: ‎2024-03-19 12:15 AM

0 Likes
0
2961
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:14 PM . Last Modified: ‎2024-03-19 12:15 AM

Hello,

The instructions are here (http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156075) on resetting the username and password. The SURT3000XLI is the UPS but you're likely accessing the UPS Network Management Card installed in it. You'll just want to double check the model - AP9619 or AP9631 most likely - so that you get the sequence correctly.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:14 PM . Last Modified: ‎2024-03-19 12:15 AM

0 Likes
0
2961
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:14 PM . Last Modified: ‎2024-03-19 12:15 AM

Can you confirm that the serial port on the ups device is actually accessing the AP9619 Network Management Card and it's the card I'm resetting.

  • Tags:
  • ap9619
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:14 PM . Last Modified: ‎2024-03-19 12:15 AM

0 Likes
0
2961
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:14 PM . Last Modified: ‎2024-03-19 12:15 AM

It sounds like it is because of the username and password prompt you're receiving. Did you confirm it is model AP9619 installed? If it is easier too, you can remove the network cable temporarily on the AP9619 (or whatever model it is) so you can focus on the single status LED that should remain on it to watch how it flashes to complete the steps.

If you have a picture of the rear, I can also tell you what I see if that helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:14 PM . Last Modified: ‎2024-03-19 12:15 AM

0 Likes
0
2961
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:14 PM . Last Modified: ‎2024-03-19 12:15 AM

dear angelna ,

                  how can we enter into SM of 3kva surt-D model .i want to change serial number of the ups be cause its change after replaced the controller card and how the calibration of these model .

thanks

best regards.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:14 PM . Last Modified: ‎2024-03-19 12:15 AM

0 Likes
0
2962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:14 PM . Last Modified: ‎2024-03-19 12:15 AM

Hi,

The SURTD model Smart-UPS have limited access over serial communications.  

The SURTD models do not support UPSLink commands like the SUA model units do. 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:14 PM . Last Modified: ‎2024-03-19 12:15 AM

0 Likes
0
2962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:14 PM . Last Modified: ‎2024-03-19 12:15 AM

Hi

I have a SURTD3000XLi and the menu is reduced as shown in the photo. I need to modify the battery constant and I cannot access the hidden menu. I did it without problems in several UPS but in this I could not. The UPS also has a network board but I tried to remove it and it didn't work either. Does anyone know how to enter the hidden menu for these cases?

Thank you
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore