SURT3000XLI Serial Not Working
  • SURT3000XLI Serial Not Working
Posted: ‎2021-06-27 11:53 PM . Last Modified: ‎2024-03-18 11:46 PM
2323
I have SURT3000XLI.When i tried to install the Powerchute Software,its not detecting the UPS.I tried with 2 cables,unfortunately both are same.Kindly help me out
Dear Bill
Hardware make:HP
Model:HP ProLiant DL380p Gen8 Intel Xeon E5-2620v2 6-Core (2.10GHz 15MB) 16GB (2 x 8GB) PC3L-12800R DDR3 1600MHz RDIMM (Low Voltage) 3 x 300GB (10k rpm) Hot Plug 2.5in Small Form Factor SC SAS Smart Array P420i/1GB FBWC DVD-RW 750W
OS: Windwos Server 2012 Standard
Power Chute: 9.1
UPS: SURTD3000XLI
Posted: ‎2021-06-27 11:54 PM . Last Modified: ‎2024-03-18 11:45 PM
Dear Bill
Problem Solved by disabling the Serial  as per the link which you provided
Thanks Bill for your kind support
Really appreciated
Cheers.smilesmilesmile
Replies 10
Angela Please reply
Keep in mind I am not the only person that contributes to the forum and have other obligations smile If you ever need an immediate response, please contact your local technical support office.
Please confirm the part numbers of the cables you tried. If it is an APC cable, the part number should be written on one of the DB-9 connectors and begin with 940-XXXX. Also, are you using any USB to serial adapters to convert the UPS serial connection to USB on your computer? Can you verify the serial port on your UPS is working properly?
Assuming you have the correct cable, you could try to talk directly to the UPS to see if it works properly. I need to make sure you have the correct cable part numbers before suggesting that and providing steps to avoid problems.
Lastly, you need to be using PowerChute Business Edition and not another variation like Personal Edition or Network Shutdown.
Thanks for your kind reply
Kindly note that we switch off the whole UPS and after sometimes switched back on.
Then deleted the Server from Powerchute and added again.It works.
Again the same problem is coming after shutdown.
Our Scenario
This UPS is in a remote site where we don't have 24 Hour Main Power Supply.
So we configured Powerchute Software to shutdown the server after 60 seconds  of power failure
We require the UPS to be off Fully so that the battery will not have any issue.
When the main power returns the UPS must start automatically and the server also
Kindly advice
When logging in through the PowerChute web interface https:///:6547 does the page loaded and does UPS show as on line?
When the UPS goes on battery depending on how you have configured PowerChute OS should be shut down and the UPS should power down.
1 - UPS goes on battery
2 - PowerChute recognizes the on battery event and start shut down count down if configured to do so
3 - Time elapses and PowerChute sends shutdown command to OS and to UPS
4 - OS completes shutdown
5 - UPS power down delay elapses and UPS goes to sleep
As for the cable, that UPS uses SKU 940-0024 or 940-1524 These are DB9 to DB9 serial cable.
Dear
The problem is that always the agent is disconnecting.
In the server log i found
 EVENT 3000APCPBEAgent
"Lost Communication With UPS"
Kindly help me to resolve this issue
Sideeque,
What is the hardware make, model of the computer, the OS, and what version of PowerChute?
Dear Bill
Hardware make:HP
Power Chute: 9.1
UPS: SURTD3000XLI
Posted: ‎2021-06-27 11:53 PM . Last Modified: ‎2024-03-18 11:45 PM
I have seen this issue with HP iLo. Review this HP document.
http://h20566.www2.hp.com/hpsc/doc/public/display?docId=emr_na-c01139344〈=en&cc=us
Dear Bill
Thanks for the reply
Serial Port is working.But after sometimes it get disconnected.Then i have to shutdown the server and switch off the UPS totally and restart the server and UPS to reconnect the Agent.
Anyway i will try the link which you provided by tomorrow and let you know the status
Thanks again for your support
Dear Bill
Really appreciated