Smart RT SURT1000XLI UPS battery configuration ?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart RT SURT1000XLI UPS battery configuration ?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-27 11:54 PM . Last Modified: ‎2024-03-18 11:45 PM

0 Likes
3
1482
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:54 PM . Last Modified: ‎2024-03-18 11:45 PM

Smart RT SURT1000XLI UPS battery configuration ?

I  own  Smart RT SURT1000XLI UPS. It supports additional  external  batteries.

Last batteries I used without additional battery pack died relatively fast.

Is it possible that UPS is configured wrong and it kills batteries thinking they are with bigger capacity (external pack added)?

I will buy new batteries, BUT I fear that if configured improperly they will die fast too.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • battery
  • config
  • external
  • settings
  • smart
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:54 PM . Last Modified: ‎2024-03-18 11:45 PM

0 Likes
0
1480
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:54 PM . Last Modified: ‎2024-03-18 11:45 PM

Hi Dave,

Yes, it is feasible that the frequent battery self tests multiple times a day could shorten the life a little bit on the batteries. I believe on this model you could use PowerChute Business Edition to disable the UPS self test which then you'd need to do it manually periodically to make sure you know when the batteries need replacing.

UPSs are designed to stay on all the time and this model is not really intended for home/office use and rather a server room where the noise is likely not as noticeable.

Let me know if you have further questions.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:54 PM . Last Modified: ‎2024-03-18 11:45 PM

0 Likes
0
1480
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:54 PM . Last Modified: ‎2024-03-18 11:45 PM

There really is no user configuration related to batteries that could cause this type of issue. The only thing you can do is maybe run too many self tests/battery calibrations. There is no user adjustment for charge voltage or similar.

If battery life is a problem, you'd want to make sure the UPS/battery environment is properly cooled and ventilated. Also consider the battery and UPS usage - do you have frequent outages for example? Lastly, when you have battery failures, especially with aging batteries (versus an isolated module failure early in life), it is recommended that you replace ALL of the batteries in the system. Mixing old and new batteries is not good and the old batteries can damage the good/new batteries on the battery bus.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:54 PM . Last Modified: ‎2024-03-18 11:45 PM

0 Likes
0
1480
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:54 PM . Last Modified: ‎2024-03-18 11:45 PM

Thank you very much for the ultra fast response.

I do not make battery tests, but turn off and on UPS every day and sometimes twice a day ...

Is it possible that on every turn on battery test is done and battery life is shortened?

The problem is that UPS is with 2 very loud fans which do work all the time and there is no way to stop noise when I do not use my computer than to shut it off completely.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:54 PM . Last Modified: ‎2024-03-18 11:45 PM

0 Likes
0
1481
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:54 PM . Last Modified: ‎2024-03-18 11:45 PM

Hi Dave,

Yes, it is feasible that the frequent battery self tests multiple times a day could shorten the life a little bit on the batteries. I believe on this model you could use PowerChute Business Edition to disable the UPS self test which then you'd need to do it manually periodically to make sure you know when the batteries need replacing.

UPSs are designed to stay on all the time and this model is not really intended for home/office use and rather a server room where the noise is likely not as noticeable.

Let me know if you have further questions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore