SURT3000XLI Internal Fault

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SURT3000XLI Internal Fault
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:49 AM . Last Modified: ‎2024-03-13 11:43 PM

0 Likes
8
1828
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:49 AM . Last Modified: ‎2024-03-13 11:43 PM

SURT3000XLI Internal Fault

Dear all,

I am facing internal fault problem with SURT3000XLI.

Whenever the UPS is powered ON it shows Internal Fault red LED & one battery charge indicator LED (green colored on extreme bottom LED).

What is the meaning of this code? Could you please tell me about the failed part from this error code, so that i can buy & replace.

My E-mail id - sajithtk@yahoo.com

Thanks in advance,

Sajith.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • help
  • please
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Clemy_apc
Crewman Clemy_apc
Crewman

Posted: ‎2021-06-29 12:50 AM . Last Modified: ‎2024-03-13 11:43 PM

0 Likes
0
1828
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:50 AM . Last Modified: ‎2024-03-13 11:43 PM

Thanks Wayne,

 

When I tested a few batteries with a voltmeter, they showed 2.5V. I assume this is to low?

The internal batteries were connected for the year with no Mains power.  The external pack was not connected at this time.

Do you know if there is a way to connect Deep Cycles batteries onto this UPS? So instead of purchasing 16 batteries I can get 2 maybe deep cycle batteries?

Just to confirm, if the batteries are unrecoverable the UPS will not start up or show any indication of power of LEDs?

 

Thanks again for your help.

 

Regards

Clemy

 

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:49 AM . Last Modified: ‎2024-03-13 11:43 PM

0 Likes
0
1828
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:49 AM . Last Modified: ‎2024-03-13 11:43 PM

HI,

Can you just cold start this UPS and see whether the "internal fault light" comes on ? . If No, then you may need to check your incoming connections and settings to ensure that it is correct. If the UPS cannot be cold start, then there could be an internal fault with the UPS itself and if it is under APC warranty, you are entitled for a unit replacement.

To cold start the UPS,

Press and hold the "On/Test" button of the UPS until you hear a long beeping sound. Upon hearing this , release the button and wait for the UPS to do a self-test. The Leds that should be on are the "On-battery" led and your battery capacity Leds. No other Leds should be on during this test.

Note: The Online Led ( green color ) will be flashing/ blinking during the self-test period but after that, it should go off.

Hope this helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:49 AM . Last Modified: ‎2024-03-13 11:43 PM

0 Likes
0
1828
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:49 AM . Last Modified: ‎2024-03-13 11:43 PM

Hi Alaska7,

In cold start also LED error indications are same like normal startup.

Regards,

Sajith.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:50 AM . Last Modified: ‎2024-03-13 11:43 PM

0 Likes
0
1828
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:50 AM . Last Modified: ‎2024-03-13 11:43 PM

I have also problems with this said, try to boot, tak tak ventilated and try to rotate, the intention of the battery is ok, I put the multimeter on the output of the batteries and 218 volt mark, but at the botom press lever test, the retention drops at 96 the same thing happens if I connect to the mains.
the only way to get it to boot is bridging the batteries, I delivered a retention of 100 volts, so it starts and then the multimeter comiensa intention to make that up, I pull the Muente and there andar.quedando comiensa to all the batteries connected .
but powering it all starts again.
from now because who can help me.
carlocaruzo@yahoo.com.ar

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:50 AM . Last Modified: ‎2024-03-13 11:43 PM

0 Likes
0
1828
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:50 AM . Last Modified: ‎2024-03-13 11:43 PM

Dear all,

I am facing internal fault problem with SURT3000XLI.

Whenever the UPS is powered ON it shows Internal Fault red LED & one battery charge indicator LED (green colored on extreme bottom LED).

What is the meaning of this code? Could you please tell me about the failed part from this error code, so that i can buy & replace.

My E-mail id - sajithtk@yahoo.com

Thanks in advance,

Sajith.

Reply

Link copied. Please paste this link to share this article on your social media post.

Clemy_apc
Crewman Clemy_apc
Crewman

Posted: ‎2021-06-29 12:50 AM . Last Modified: ‎2024-03-13 11:43 PM

0 Likes
0
1828
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:50 AM . Last Modified: ‎2024-03-13 11:43 PM

Hi All,

 

I have a SURT3000XLI with the external battery pack that was working 2 years ago. My client hasn’t used it in the last year, I decided to test it and try and use it. But when I plug in the main power and press the ON button nothing happens.

If the batteries are stone cold dead, will the UPS start up at all? Or even will it show any sign of power going through the UPS?

 

If it is the batteries, will I need purchase all 16 for both banks? Or can I use 1 bank to test?

 

Further to this, not sure if possible. But will I be able to connect this UPS with deep cycle batteries?

If someone could assist me, would really appreciate it.

 

Thanks Guys.

Regards

Clemy

  • Tags:
  • 3000
  • apc
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

wayne_i_apc
Lieutenant wayne_i_apc
Lieutenant

Posted: ‎2021-06-29 12:50 AM . Last Modified: ‎2024-03-13 11:43 PM

0 Likes
0
1828
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:50 AM . Last Modified: ‎2024-03-13 11:43 PM

Hi Clemy,

If the batteries are lower than some minimum voltage (I recall reading that it is something around 180 volts), the UPS will not power on, even with good Mains power. Have you confirmed the batteries are, as you say "stone, cold dead" with a voltmeter, and that both battery connectors are securely plugged in? Also, unfortunately, I don't believe the batteries will be able to be charged by the UPS unless they have at least the minimum voltage to start.

If the batteries were left connected for the year that the unit wasn't used, and I assume not connected to Mains power, they are probably unrecoverable, and strings (or banks of 2 modules) you replace should be replaced as a full set of 16. The UPS has 2 internal battery modules and an external battery pack has 4 more modules. The UPS requires 2 modules (or a "string" of 16 batteries) to operate, so you could replace and connect ONLY the 2 internal modules (be sure the old, dead external batteries are disconnceted) to confirm operation of the UPS although it wiil have a shortened run time in this state.

Reply

Link copied. Please paste this link to share this article on your social media post.

Clemy_apc
Crewman Clemy_apc
Crewman

Posted: ‎2021-06-29 12:50 AM . Last Modified: ‎2024-03-13 11:43 PM

0 Likes
0
1829
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:50 AM . Last Modified: ‎2024-03-13 11:43 PM

Thanks Wayne,

 

When I tested a few batteries with a voltmeter, they showed 2.5V. I assume this is to low?

The internal batteries were connected for the year with no Mains power.  The external pack was not connected at this time.

Do you know if there is a way to connect Deep Cycles batteries onto this UPS? So instead of purchasing 16 batteries I can get 2 maybe deep cycle batteries?

Just to confirm, if the batteries are unrecoverable the UPS will not start up or show any indication of power of LEDs?

 

Thanks again for your help.

 

Regards

Clemy

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

wayne_i_apc
Lieutenant wayne_i_apc
Lieutenant

Posted: ‎2021-06-29 12:50 AM . Last Modified: ‎2024-03-13 11:43 PM

0 Likes
0
1828
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:50 AM . Last Modified: ‎2024-03-13 11:43 PM

This model UPS needs 2 modules, each module providing about 96 volts, for the UPS to show any signs of life.

Each of the individual batteries within a module should read about 12 volts, so yes, any that read 2.5 volts are probably useless by now (please recycle!). If the external batteries were disconnected, you should check the voltage at the connectors that would plug into the main UPS unit. Each of those connectors should read close to 92 - 96 volts if the batteries have any life left, as they might since they have been disconnected for the past year. If you find 2 modules in the external battery cabinet with a voltage in this range, you could use them to try operating the UPS.

If you want to try being creative and substituting non-standard batteries, ANY arrangement of batteries will need to add up to 96 volts at the connector from the module that plugs into the UPS, so for 12 volt batteries (the most common type you can buy), you will need 8 batteries wired "in series" to produce the 96 volts needed, and you will need 2 of those arrangements connected to the UPS to replace the 2 original battery modules for the UPS to operate. I can't imagine there are any 96 volt batteries for sale that would allow you to buy only 2... Please also keep in mind there are potentially very dangerous voltages and currents produced by these modules or any configuration you create to replace a module, so be extremely careful!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore