SURT20KRMXLT-1TF10K installation
sorry guys, problem is explained in spanish but i think because the numbers you will get some info, UPS work great with energy, when energy loss, the problems begin
**********************************************************************
Hemos instalado un UPS surt20krmxlt con transformador de 10 KVA y se ha seguido las indicaciones del manual, es decir:
• Entrada del Transformador: 240 voltios (L1, L2 y GND) en con selector de voltaje de 220-240 voltios conectado en bornera (L1, L2/N, GND)
• Salida del transformador: 240 voltios en bornera (7 y 10 para fases, 8 para neutro con puente en 8 y GND)
• Entrada UPS: 240 voltios con borne 7 del transformador a L1, borne 10 a L2 y borne 8 a N. las medidas son de 240 entre L1 y L2 y de 120 entre L1-N y L2-N
• Salida del UPS : con OSJ conectado, L1 a una fase del tablero de UPS, L2/N a otra fase del tablero UPS y N a borne de neutro
El modulo de batería está conectado de acuerdo a manual
Se tomaron mediciones con equipo Fluke 322 true RMS en condición de UPS apagado, encendido y en falla de suministro en la carga y los resultados son los siguientes:
UPS APAGADO (solo alimentación del transformador)
L1-N = 115 VOLTIOS
L2-N =116 VOLTIOS
L1-L2 = 0 VOLTIOS
Operacion anormal ya que la salida debe ser de 0 voltios
?
PRUEBA CON INTERRUPCION DE ENERGIA
L1-N = 233 VOLTIOS
L2-N =6.7 VOLTIOS
L1-L2 = 239 VOLTIOS
LED ENCENDIDOS: LOAD ON, LOAD BAT, FAULT
Falla anormal la salida debe ser de 240/120
**************************