Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

SURT2000XLI Internal Fault

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SURT2000XLI Internal Fault
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:37 AM . Last Modified: ‎2024-03-12 11:19 PM

0 Likes
8
1420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:37 AM . Last Modified: ‎2024-03-12 11:19 PM

SURT2000XLI Internal Fault

Hi there,

I purchased a surt2000xl that had never been used and finally got it out of the box today.

I connected it as per the instructions and plug in the power.

#1 - I am getting an internal fault, with the second and third less (counting form the bottom) flashing.

What is that fault code?

I checked the batteries and one is at 6v the others at around 12. I am charging the low battery now.

#2 - I have now tried to power on the unit without the battery and it doesn't power on at all. Is that normal?

Thanks

Matty

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 2000xli
  • fault
  • smart-ups
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:38 AM . Last Modified: ‎2024-03-12 11:12 PM

0 Likes
0
1420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:38 AM . Last Modified: ‎2024-03-12 11:12 PM

Thanks so much, lets hope it's a minor fault compared to others I have read about here

I will let you know my findings

Matty

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:38 AM . Last Modified: ‎2024-03-12 11:19 PM

0 Likes
0
1420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:38 AM . Last Modified: ‎2024-03-12 11:19 PM

Hello,

On # 1 could you please use the picture below to verify what you see? I just want to be really sure I understand what is solid and flashing.

1376_smartupsRTFront.jpg

# 2 - Yes, these SURT UPSs require good batteries to power on.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:38 AM . Last Modified: ‎2024-03-12 11:19 PM

0 Likes
0
1420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:38 AM . Last Modified: ‎2024-03-12 11:19 PM

Hi Angela

First - thanks for answering so quickly. See picture for details.....

I am getting a flashing red led over the X, that is the middle led above the on button.

I am getting 2 flashing less above the battery symbol. Not the bottom led but the 2 above it.

All of these a flashing together not very fast.

I am still charging the bad battery, when It gets to 12 volts I will reassamble and retry

Thanks

Matty

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:38 AM . Last Modified: ‎2024-03-12 11:19 PM

0 Likes
0
1420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:38 AM . Last Modified: ‎2024-03-12 11:19 PM

I looked this fault up and it says its a Fan Fault. You could try cleaning the fan with some compressed air or make sure it looks okay (like make sure nothing is preventing it from spinning).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:38 AM . Last Modified: ‎2024-03-12 11:19 PM

0 Likes
0
1420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:38 AM . Last Modified: ‎2024-03-12 11:19 PM

Angela

Thanks again,

I was mistaken, the power to the fan was working when I ran a self test.

My assumption now is the fan is not behaving as it should, so I ordered two new ones from Hong Kong and when they come i will install them.

I will let you know if it does the trick.

Funny thing is I actually bought this unit in the US, but I have had it shipped to the middle eat.

Regards

Matty

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:38 AM . Last Modified: ‎2024-03-12 11:19 PM

0 Likes
0
1420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:38 AM . Last Modified: ‎2024-03-12 11:19 PM

Angela

I found the 2 fans in the unit (one is on the front and one on the back blowing air over the huge heatsink.

It appears that the power to the rear fan is not good. The fan itself works fine (I swapped it with the front one and it span just fine).

Any ideas what causes the fan power supply to fail? Where should I look next?

Thanks

Matty

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:38 AM . Last Modified: ‎2024-03-12 11:19 PM

0 Likes
0
1420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:38 AM . Last Modified: ‎2024-03-12 11:19 PM

As far as I know, these are not really serviceable but it depends on region how this type of thing is handled. So in the USA where I am, we'd have a user replace the entire unit either under warranty (at our cost) or outside of warranty. I am going to assume you are not in the USA since the SKU we are discussing is international.

We also do not provide schematics or anything so I won't be all that helpful with the internal workings of the unit and what to do at that level.

If anyone wants to help here on the forum, that's fine and it'd be at your own risk but for any other options locally (repair, check warranty status, etc), I'd contact your local technical support team who may be able to make further recommendations.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:38 AM . Last Modified: ‎2024-03-12 11:18 PM

0 Likes
0
1420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:38 AM . Last Modified: ‎2024-03-12 11:18 PM

Well I hope it is as simple as new fans and you're able to fix it! (I always personally think it is a shame that type of thing is not easily serviceable by everyone for larger units).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:38 AM . Last Modified: ‎2024-03-12 11:12 PM

0 Likes
0
1421
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:38 AM . Last Modified: ‎2024-03-12 11:12 PM

Thanks so much, lets hope it's a minor fault compared to others I have read about here

I will let you know my findings

Matty

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of