SURT10KRMXL + SURT192XLBP => Giving me grief

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SURT10KRMXL + SURT192XLBP => Giving me grief
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
114
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:55 PM . Last Modified: ‎2024-03-06 03:34 AM

0 Likes
2
860
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:55 PM . Last Modified: ‎2024-03-06 03:34 AM

SURT10KRMXL + SURT192XLBP => Giving me grief

SURT10KRMXL + SURT192XLBP

The unit has started throwing low battery alarms, yet when I measure the battery voltages (8 cartridges in total) they appear to be within spec.

107 108 108 108
108 107 106 105


Battery Capacity shows as 100% in the status overview, but the reported run-time on a load that varies from 34-37% is only about 6-7mins (2min low duration)

Clearly, something is wrong.

So... starting with the simple stuff...

UPS>Configuration>General>External_Batteries  = 1

Is this correct ??

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • surt10krmxl
  • surt192xlbp
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:55 PM . Last Modified: ‎2024-03-06 03:34 AM

0 Likes
0
860
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:55 PM . Last Modified: ‎2024-03-06 03:34 AM

Thanks for that.

Yes, it's confusing as to what is 'external' and what is 'internal' given that the SURT10KRMXL is a single unit that includes a set of batteries, which it apparently considers to be 'external' !?

So anyway, I reset the External Batteries to 2 and now have a estimated run-time of 15mins.

I'm hoping that is real, as it at least provides for graceful shutdown, but will schedule a calibration test when I get a chance.

This is still well below the 30-35mins that the on-line charts indicate I should expect for that load, but I am aware that the batteries are approaching their end of their life.

Could battery age have any affect on the estimate, despite the measured voltage being within spec ?

Also, another related question...

UPS>Configuration>Shutdown>End_of_Shutdown>Minimum_Battery_Capacity = nn%

Does the UPS take this into account when calculating run-time ?

I wouldn't have thought so, but someone had set this to 40% and I noticed that when I dropped it to 0% the number of low-battery warnings suddenly dropped significantly... which I find strange. Perhaps it was just coincidence ??

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:55 PM . Last Modified: ‎2024-03-06 03:34 AM

0 Likes
0
860
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:55 PM . Last Modified: ‎2024-03-06 03:34 AM

Hey Mike,

Check your custom alarm settings, sometimes these can be set to high. (simple, but not really what your looking for)

This KBase explains how to add external battery backs. It can be a little tricky and it is dependant on firmware version. 

http://www2.schneider-electric.com/sites/corporate/en/support/faq/faq_main.page?page=content&country...=en&locale=en_US&id=FA156601&redirect=true

Also you may want to try a run time calibration (this has worked for other customer of mine in the past). This Kbase explains some options, I would read the entire thing but "Option 3: Perform a Manual Runtime Calibration." is what im talking about. I stress that this is something you should do during down time. It has the potential to drop your load.

http://www2.schneider-electric.com/sites/corporate/en/support/faq/faq_main.page?page=content&country...=en&locale=en_US&id=FA156538&redirect=true

Tom

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:55 PM . Last Modified: ‎2024-03-06 03:34 AM

0 Likes
0
861
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:55 PM . Last Modified: ‎2024-03-06 03:34 AM

Thanks for that.

Yes, it's confusing as to what is 'external' and what is 'internal' given that the SURT10KRMXL is a single unit that includes a set of batteries, which it apparently considers to be 'external' !?

So anyway, I reset the External Batteries to 2 and now have a estimated run-time of 15mins.

I'm hoping that is real, as it at least provides for graceful shutdown, but will schedule a calibration test when I get a chance.

This is still well below the 30-35mins that the on-line charts indicate I should expect for that load, but I am aware that the batteries are approaching their end of their life.

Could battery age have any affect on the estimate, despite the measured voltage being within spec ?

Also, another related question...

UPS>Configuration>Shutdown>End_of_Shutdown>Minimum_Battery_Capacity = nn%

Does the UPS take this into account when calculating run-time ?

I wouldn't have thought so, but someone had set this to 40% and I noticed that when I dropped it to 0% the number of low-battery warnings suddenly dropped significantly... which I find strange. Perhaps it was just coincidence ??

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of