SMX3000 + SMX120: Which battery failed?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMX3000 + SMX120: Which battery failed?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:55 PM . Last Modified: ‎2024-03-06 03:28 AM

0 Likes
1
1250
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:55 PM . Last Modified: ‎2024-03-06 03:28 AM

SMX3000 + SMX120: Which battery failed?

Hello,

we do have an SMX3000RMHV2U. About half a year later we added one SMX120RMBP2U. Now we are going to add another one.

Question:
The SMX3000RMHV2U got an indicator that shows us that we need to replace the battery and shows battery failures (& via NMC2).
In this setup we have many batteries and these batteries are of different ages and in different enclosures - but they are all connected together.
How can we tell which battery we do have to replace? There does not need to be a correlation between age and failure.

It seems very uneconomical and environmentally absolutely unacceptable to replace all batteries, only because we can not tell which battery needs replacement.

Can anyone tell us how to find out which battery to replace? (Without changing/replacing batteries one by one, which is unacceptable, too.)

Thanks a lot!
-RT

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • battery
  • failed
  • fault
  • replace
  • replacement
  • smart-ups
  • smx120rmbp2u
  • smx3000rmhv2u
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
MarkC_apc
Commander MarkC_apc
Commander

Posted: ‎2021-06-30 10:55 PM . Last Modified: ‎2024-03-06 03:28 AM

0 Likes
0
1250
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:55 PM . Last Modified: ‎2024-03-06 03:28 AM

The SMX3000 has an interesting battery pack of 10 small AGMs - all in series with relatively (to other APC UPSs) complicated interconnecting wiring and spacers (nominal 120 volt DC).  WARNING - this is a high level of DC voltage and can be very dangerous/deadly with powerful arc potential.  Replacing individual batteries (if you can determine which are bad) in this pack can be a challenge!

Adding the extended battery units essentially adds multiples of these packs in parallel with the one contained in the main unit.   This arrangement of the packs in parallel - with each containing many batteries in series requires that all batteries be essentially the same in their electrical characteristics - otherwise the weakest battery in the entire system will essentially drag the entire battery system to it's (weak) level.  

Running an identical load test on each fully charged pack individually might tell you if one of the three packs you currently have is bad (or substantially reduced energy), but could require a significant time without the protection of the UPS if done with a known external load.  If the age of the original pack is nearing it's life expectancy (2-3 years?) and/or has been through many power failure cycles, you might try a new pack in addition to the new SMX120 unit. 

Of course, if any warantees exist - see what Schneider can recommend.  There may also be a recommended testing procedure for multiple packs as you have.

There are methods to determine if individual AGM batteries are bad.  However, in usual critical services, it is best to replace the entire pack as explained in the second paragraph.

Let me know how you resolve this.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
MarkC_apc
Commander MarkC_apc
Commander

Posted: ‎2021-06-30 10:55 PM . Last Modified: ‎2024-03-06 03:28 AM

0 Likes
0
1251
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:55 PM . Last Modified: ‎2024-03-06 03:28 AM

The SMX3000 has an interesting battery pack of 10 small AGMs - all in series with relatively (to other APC UPSs) complicated interconnecting wiring and spacers (nominal 120 volt DC).  WARNING - this is a high level of DC voltage and can be very dangerous/deadly with powerful arc potential.  Replacing individual batteries (if you can determine which are bad) in this pack can be a challenge!

Adding the extended battery units essentially adds multiples of these packs in parallel with the one contained in the main unit.   This arrangement of the packs in parallel - with each containing many batteries in series requires that all batteries be essentially the same in their electrical characteristics - otherwise the weakest battery in the entire system will essentially drag the entire battery system to it's (weak) level.  

Running an identical load test on each fully charged pack individually might tell you if one of the three packs you currently have is bad (or substantially reduced energy), but could require a significant time without the protection of the UPS if done with a known external load.  If the age of the original pack is nearing it's life expectancy (2-3 years?) and/or has been through many power failure cycles, you might try a new pack in addition to the new SMX120 unit. 

Of course, if any warantees exist - see what Schneider can recommend.  There may also be a recommended testing procedure for multiple packs as you have.

There are methods to determine if individual AGM batteries are bad.  However, in usual critical services, it is best to replace the entire pack as explained in the second paragraph.

Let me know how you resolve this.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of