SURT1000XLI failure?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SURT1000XLI failure?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:48 PM . Last Modified: ‎2024-03-06 10:38 PM

0 Likes
2
1141
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:48 PM . Last Modified: ‎2024-03-06 10:38 PM

SURT1000XLI failure?

I wonder if anyone in this community could help me.

I have a Smart UPS RT1000 that is driving me nuts...  Story from the start:

Since purchase, over time time battery strength indicator goes from 5 to 2 lights and finally, get the alarm saying battery is dead please replace.  The unit is 4 years old so not too bad - thus purchase a new battery.

Install new battery, get my 2 lights on battery strength and by the end of the day i have 5 lights - great. And then following morning down to 2 lights for battery strength.  Assume it was just a surface charge and that the UPS will recharge the battery.

2 days later still 2 lights so using Powerchute console have a look and says battery is 50 volts, charge 27% and will last 14 minutes without power.  So I pull the plug to test, and after 2 mins shutdown.....

Phone support in France and they say - out of warranty, buy a new one.....

Do some googling and then do the Hyperterminal reset for new battery, recharge the batteries outside the unit and start again - same result. 

So after a lot of testing, if I put fully charged battery unit in with 52 volts on the meter, the following day it is down to 47 volts.... though Powerchute software says the minimum it reaches is 50 volts......  At this stage i notice that even with battery disconnected, I still have 2 lights light for battery charge, and no reaction from the UPS saying the battery is missing.....  Powerchute software doesn't seem to notice either that there is no battery......

Volt meter on the UPS battery connector shows 47.2 volts and implies the UPS is not sending enough voltage to charge the battery.....apparently it should output closer to 57 volts to charge the battery?  Can this be adjusted somehow?

I am in France and the support is pretty much - remove battery, pull power on unit and let is reset, then put in battery and power up unit.  Oh, that didn't work, erh, well buy a new one....  At Euros 1100 odd that is pretty diabolical support and they have no repair service either.  As a professional product for a businees to ensure reliability of servers, I must say I am more than disappointed....

Anyone have any thoughts on this - thanks.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:48 PM . Last Modified: ‎2024-03-06 10:38 PM

0 Likes
0
1140
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:48 PM . Last Modified: ‎2024-03-06 10:38 PM

Ed,

Sorry to hear of the inconvenience. 

On 12/2/2015 3:19 AM, Ed said:

Volt meter on the UPS battery connector shows 47.2 volts and implies the UPS is not sending enough voltage to charge the battery.....apparently it should output closer to 57 volts to charge the battery?  Can this be adjusted somehow?

The charging circuitry cannot be adjusted.  

On 12/2/2015 3:19 AM, Ed said:

I am in France and the support is pretty much - remove battery, pull power on unit and let is reset, then put in battery and power up unit.  Oh, that didn't work, erh, well buy a new one....  At Euros 1100 odd that is pretty diabolical support and they have no repair service either.  As a professional product for a business to ensure reliability of servers, I must say I am more than disappointed....

We do not offer a repair service however we do offer the trade-UPS program where you trade in you used UPS for a discount on a new UPS. The trade-UPS program work better for most customer since you do not do not have to wait for the repair. You purchase the UPS model through the program and are shipped the new UPS. After receiving the new unit you will send the old unit to Schneider Electric for recycling.  

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:48 PM . Last Modified: ‎2024-03-06 10:38 PM

0 Likes
0
1140
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:48 PM . Last Modified: ‎2024-03-06 10:38 PM

I thought there might at least have been APC admin who might have commented.......

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:48 PM . Last Modified: ‎2024-03-06 10:38 PM

0 Likes
0
1141
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:48 PM . Last Modified: ‎2024-03-06 10:38 PM

Ed,

Sorry to hear of the inconvenience. 

On 12/2/2015 3:19 AM, Ed said:

Volt meter on the UPS battery connector shows 47.2 volts and implies the UPS is not sending enough voltage to charge the battery.....apparently it should output closer to 57 volts to charge the battery?  Can this be adjusted somehow?

The charging circuitry cannot be adjusted.  

On 12/2/2015 3:19 AM, Ed said:

I am in France and the support is pretty much - remove battery, pull power on unit and let is reset, then put in battery and power up unit.  Oh, that didn't work, erh, well buy a new one....  At Euros 1100 odd that is pretty diabolical support and they have no repair service either.  As a professional product for a business to ensure reliability of servers, I must say I am more than disappointed....

We do not offer a repair service however we do offer the trade-UPS program where you trade in you used UPS for a discount on a new UPS. The trade-UPS program work better for most customer since you do not do not have to wait for the repair. You purchase the UPS model through the program and are shipped the new UPS. After receiving the new unit you will send the old unit to Schneider Electric for recycling.  

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore