Hi,
I am running an APC SMART 3000 RT - SURTD3000XLI - rack mounted with an extended battery pack . There is a AP9630 NMC in the UPS, where can I find the latest firmware for the device?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:48 PM . Last Modified: 2024-03-06 10:38 PM
Hi Riyaaz,
You are getting lost comms with the UPS because you have the symmetra application version of the firmware. To re establish the communication download the smart-ups/matricx application and upgrade the firmware.
Go to the firmware page on this link and download part number SFSUMX621 Probably easiest to just control f the part number to make sure you grab the correct download.
http://www.apc.com/shop/us/en/products/UPS-Network-Management-Card-2/P-AP9630
Regards,
Mike
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:48 PM . Last Modified: 2024-03-06 10:38 PM
Hi,
SURTD Smart-UPS do not have upgradeable firmware. Smart-UPS that have upgradeable firmware are models SMT, SMX, SRT.
You will find the latest firmware for the AP9630 at this link by selecting Upgrade Firmware: Network Management Card from the Filter by Software / Firmware drop down. http://www.apc.com/tools/download/index.cfm
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:48 PM . Last Modified: 2024-03-06 10:38 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:48 PM . Last Modified: 2024-03-06 10:38 PM
Hi Bill, thank you for your reply,however after upgrading the NMC , it indicates that it has lost comms to the UPS. How do i establish comms with the UPS, also it indicates Symmetra Application in the top of the NMC web interface instead of Smart-UPS/Matrix Application , as per the other UPS we have on-site.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:48 PM . Last Modified: 2024-03-06 10:38 PM
Hi Riyaaz,
You are getting lost comms with the UPS because you have the symmetra application version of the firmware. To re establish the communication download the smart-ups/matricx application and upgrade the firmware.
Go to the firmware page on this link and download part number SFSUMX621 Probably easiest to just control f the part number to make sure you grab the correct download.
http://www.apc.com/shop/us/en/products/UPS-Network-Management-Card-2/P-AP9630
Regards,
Mike
Link copied. Please paste this link to share this article on your social media post.