SURT1000XLI disaster

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SURT1000XLI disaster
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-07-07 10:15 PM . Last Modified: β€Ž2024-03-04 10:51 PM

0 Likes
4
4334
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-07 10:15 PM . Last Modified: β€Ž2024-03-04 10:51 PM

SURT1000XLI disaster

What do you think?

%2BbvYbjSF%2BCOzO2Ykqtj0hw%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg%2BbvYbjSF%2BCOzO2Ykqtj0hw%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg

BYYJiWEiNfpD42XP5jRa1Q%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpegBYYJiWEiNfpD42XP5jRa1Q%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg

yvTjbiA08%2BDt9Kt5G6HiUg%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpegyvTjbiA08%2BDt9Kt5G6HiUg%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg

BRaT1KdEf7FwFOBw8CmFOA%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpegBRaT1KdEf7FwFOBw8CmFOA%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg

TjQLMTmdqA4Yopj0jFLgaA%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpegTjQLMTmdqA4Yopj0jFLgaA%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg

JSV%2FZqX3BY3ylTG5ypPicg%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpegJSV%2FZqX3BY3ylTG5ypPicg%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg

MXA71r0zvfokSuoQa2Od%2Fw%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpegMXA71r0zvfokSuoQa2Od%2Fw%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg

cNRi6F5MH3u8%2Fu5V08BWvA%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpegcNRi6F5MH3u8%2Fu5V08BWvA%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg

%2FyRVLft5P9CwqeHMJbdArw%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg%2FyRVLft5P9CwqeHMJbdArw%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-07-07 10:15 PM . Last Modified: β€Ž2024-03-04 10:51 PM

0 Likes
0
4334
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-07 10:15 PM . Last Modified: β€Ž2024-03-04 10:51 PM

if you were satisfied with this model, my suggestion is, as i always suggest people; "buy the same one" and leave this  you have for spare parts in case the new one goes wrong....at least you will have some spare parts and make it cheaper and easier to electronic technician when repairing eventually....unless the new one burns exactly the same way like yours now....but lets hope it wont be the case πŸ™‚

wish you Happy Easter πŸ˜‰

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: β€Ž2021-07-07 10:15 PM . Last Modified: β€Ž2024-03-04 10:51 PM

0 Likes
0
4333
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-07 10:15 PM . Last Modified: β€Ž2024-03-04 10:51 PM

That doesn't look good. I've seen parts fail in APC (and other brand) UPSs, but not to that extent. Assuming it "just happened" during normal operation, as opposed to being shot with a large-caliber weapon, or coming back from "Ugly Ed's Video Repair Emporium" after "repair", then I would think APC would be very interested in finding out what went wrong. I'd suggest contacting your appropriate APC support office, asking to speak to an engineer, and describe the problem (and pictures) to them and request a "failure analysis" in addition to repair/replace (if it is in warranty). If it is something that APC could investigate and prevent happening in future models, I expect this will work out well for both of you. If you can't get to anyone who knows what failure analysis is, post back in this topic and Angela will see it and point you at an appropriate contact. To help her with that, you might want to mention the region is was purchased in (for example, Canada) and the region it was used in (for example, the USA). That will let her direct you to the most appropriate contact.

It is usually best to "preserve the evidence" if you are going to send something (anything) for failure analys, meaning not disassembling anything more than needed to make the unit safe (generally isolating the batteries) and definitely not cleaning any of the scorched areas. The pattern of the scorching and the stuff deposited provide important leads as to what happened, and in what sequence of steps.

As an aside, a UPS contains a lot of high-energy components (batteries, capcacitors, etc.) which means that even when external power is removed, there is still a lot of stored power in the UPS. Combined with the necessarily sensitive and accurate electronics in there, if something shorts out, lots of bad things can happen.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-07-07 10:15 PM . Last Modified: β€Ž2024-03-04 10:51 PM

0 Likes
0
4333
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-07 10:15 PM . Last Modified: β€Ž2024-03-04 10:51 PM

IMHO: the problem was caused by MKP capacitor in EMI filter section at the input of mains.....see this yellow capacitor.....it is Metalised Polypropylene capacitor...it brokethrough (went short) and got overheated up to the "eruption" it causes sparks while working under higher voltage that was up to 350V....and the rest is as you can see...

if you are about to repair it, for 1000VA UPS 3.3uF/400V is enough....and rest as it was originally...and burned spots, wires, simply bypass with new lines, wires...

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-07-07 10:15 PM . Last Modified: β€Ž2024-03-04 10:51 PM

0 Likes
0
4333
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-07 10:15 PM . Last Modified: β€Ž2024-03-04 10:51 PM

I'm from Argentina (sorry about my bad english) and this ups was connected to 220v during years.

The ups work fine over all those years and i think the cost of repair the unity is very high.

The card of the brown slot is totaly out.

Maybe is better buy a new one.

Thanks for the answers guys.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-07-07 10:15 PM . Last Modified: β€Ž2024-03-04 10:51 PM

0 Likes
0
4335
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-07 10:15 PM . Last Modified: β€Ž2024-03-04 10:51 PM

if you were satisfied with this model, my suggestion is, as i always suggest people; "buy the same one" and leave this  you have for spare parts in case the new one goes wrong....at least you will have some spare parts and make it cheaper and easier to electronic technician when repairing eventually....unless the new one burns exactly the same way like yours now....but lets hope it wont be the case πŸ™‚

wish you Happy Easter πŸ˜‰

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore