SURT10000XLT Uneven battery discharging

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SURT10000XLT Uneven battery discharging
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:50 AM . Last Modified: ‎2024-03-13 12:25 AM

0 Likes
3
1061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:50 AM . Last Modified: ‎2024-03-13 12:25 AM

SURT10000XLT Uneven battery discharging

I have a SURT10000XLT purchased in 2006 or 2007. Yesterday it failed with an inverter fault, switched to batteries, shut down the servers and turned off. I came in and the room smelled of sulfur, made me suspect battery issues. Found a small leak. The unit has three external battery units plus the one internal for 16 battery packs total. The eight oldest ones were clearly unusable, some were leaking and all read out very low voltages. But the eight newest ones are a different story. There are two sets of four, each set purchased at the same time. In both of those sets, the two left-most batteries were discharged, and the two right-most batteries were fully charged (102-104V). I verified the inverter fault was related to the bad batteries by disconnecting the external units, putting the four good batteries into the internal battery slots in the chassis, and firing it up. It ran with no problems or faults and completed a self-test.

Now the question: Can I safely conclude that the problem was the batteries and that the UPS is ok? Our power consumption has decreased since the unit was purchased so I feel safe running on two battery units instead of four. But how to explain the uneven discharging? We have two step-down transformers connected. There are four outputs on the back. The fact that only two of the four outputs are in use and that only two of the four batteries were discharged makes me suspect that may be the explanation. But if there's something wrong with the UPS (i.e. it isn't charging all the batteries properly) I don't want to put all our equipment back onto it until the issue is resolved. Thoughts?

-Joe

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:50 AM . Last Modified: ‎2024-03-13 12:25 AM

0 Likes
0
1059
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:50 AM . Last Modified: ‎2024-03-13 12:25 AM

This UPS comes with a preinstalled management card. Is that configured and available on the network? Are we able to download event.txt, data.txt and config.ini from it? It'd be good if we can review the logs from the system to see if there are any faults in there. I am hoping since you knew there was an inverter fault, you got that message from the management card?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:50 AM . Last Modified: ‎2024-03-13 12:25 AM

0 Likes
0
1059
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:50 AM . Last Modified: ‎2024-03-13 12:25 AM

If the UPS is on the network (which I assume it is since you're using telnet to access it), you can FTP to it and get the log files - instructions are in the knowledge base (http://www.apc.com/site/support/index.cfm/faq/) and search for article ID FA156131. We'll need at least data.txt and event.txt as noted in the instructions.

Anyway, if you saw inverter fault and it cleared, I'd say that is the issue which could be causing other problems but the logs can help me analyze further.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:50 AM . Last Modified: ‎2024-03-13 12:25 AM

0 Likes
0
1059
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:50 AM . Last Modified: ‎2024-03-13 12:25 AM

I have a SURT10000XLT purchased in 2006 or 2007. Yesterday it failed with an inverter fault, switched to batteries, shut down the servers and turned off. I came in and the room smelled of sulfur, made me suspect battery issues. Found a small leak. The unit has three external battery units plus the one internal for 16 battery packs total. The eight oldest ones were clearly unusable, some were leaking and all read out very low voltages. But the eight newest ones are a different story. There are two sets of four, each set purchased at the same time. In both of those sets, the two left-most batteries were discharged, and the two right-most batteries were fully charged (102-104V). I verified the inverter fault was related to the bad batteries by disconnecting the external units, putting the four good batteries into the internal battery slots in the chassis, and firing it up. It ran with no problems or faults and completed a self-test.

Now the question: Can I safely conclude that the problem was the batteries and that the UPS is ok? Our power consumption has decreased since the unit was purchased so I feel safe running on two battery units instead of four. But how to explain the uneven discharging? We have two step-down transformers connected. There are four outputs on the back. The fact that only two of the four outputs are in use and that only two of the four batteries were discharged makes me suspect that may be the explanation. But if there's something wrong with the UPS (i.e. it isn't charging all the batteries properly) I don't want to put all our equipment back onto it until the issue is resolved. Thoughts?

-Joe

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:50 AM . Last Modified: ‎2024-03-13 12:25 AM

0 Likes
0
1060
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:50 AM . Last Modified: ‎2024-03-13 12:25 AM

This UPS comes with a preinstalled management card. Is that configured and available on the network? Are we able to download event.txt, data.txt and config.ini from it? It'd be good if we can review the logs from the system to see if there are any faults in there. I am hoping since you knew there was an inverter fault, you got that message from the management card?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore