SURT10000XLI - power consumption is needed for battery charge

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SURT10000XLI - power consumption is needed for battery charge
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-27 11:33 PM . Last Modified: ‎2024-03-19 12:05 AM

0 Likes
5
1685
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:33 PM . Last Modified: ‎2024-03-19 12:05 AM

SURT10000XLI - power consumption is needed for battery charge

Hi Everyone,

I've tried Google or product documentation, forum but cannot find. Please help to answer:

- Can i know how much consumption is needed for battery charge without device?

Reason: Beside device load, i also need calculate that value to request building management provide suitalbe power source, circuit breaker, electric wire condition as well.

Appreciate any help.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:33 PM . Last Modified: ‎2024-03-19 12:05 AM

0 Likes
0
1685
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:33 PM . Last Modified: ‎2024-03-19 12:05 AM

This UPS has an 800W battery charger it appears. So if the UPS is charging fully discharged batteries, it'd use the 800W charger and then as it gets close to 100% charge, start to trickle charge. Also, the documentation says it has 92% efficiency.

The recommended breaker size for the UPS should take all of this into account and also for a potential overload sizing I think.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:34 PM . Last Modified: ‎2024-03-19 12:05 AM

0 Likes
0
1685
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:34 PM . Last Modified: ‎2024-03-19 12:05 AM

Hi Dzung,

We have a tool call the UPS Efficieny Calculator. What it will do is tell you the UPS losses at any load. In the screenshot below, I've dropped the load down to 0 (and mind you, I am comparing the UPS to itself) and you can see it says the losses are about 185 Watts so that would be the answer to your question.

A link to this tool is here: http://www.apc.com/tool/?tt=5

8CjIwCLBOlsJtHEGUNElDA%3D%3D.jpeg8CjIwCLBOlsJtHEGUNElDA%3D%3D.jpeg

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:33 PM . Last Modified: ‎2024-03-19 12:05 AM

0 Likes
0
1686
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:33 PM . Last Modified: ‎2024-03-19 12:05 AM

This UPS has an 800W battery charger it appears. So if the UPS is charging fully discharged batteries, it'd use the 800W charger and then as it gets close to 100% charge, start to trickle charge. Also, the documentation says it has 92% efficiency.

The recommended breaker size for the UPS should take all of this into account and also for a potential overload sizing I think.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:34 PM . Last Modified: ‎2024-03-19 12:05 AM

0 Likes
0
1685
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:34 PM . Last Modified: ‎2024-03-19 12:05 AM

Hi Angela,

Thank you for helpful answer.

Could you share:

- document related with "800W battery charger" and "92% efficiency"?

- the current (amps) for this battery charger (My guess is 3 amps)?

Please forgive for my annoying...

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:34 PM . Last Modified: ‎2025-05-27 11:31 PM

0 Likes
0
1685
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:34 PM . Last Modified: ‎2025-05-27 11:31 PM

Hi Dzung,

I just realized I mis-read the model number you provided me. I looked up SRT10000XLI, not SURT10000XLI. SRT is the newer generation of the model you have. Though, the answers should be similar...

You can find the efficiency and a little graph listed here for your model: https://www.se.com/ca/en/product/SURT10000XLI/

I also only have an internal specification document telling me that the Maximum Input Current is 68A during 160V Bypass with battery charging. But I did confirm SURT10000XLI also contains an 800W charger, and Charging current (Amps) is listed as ~2 Amps.

I hope this helps. If you need a more formal document/specification sheet, I'd have to suggest you contact your local technical support office to see what they can provide.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:34 PM . Last Modified: ‎2024-03-19 12:05 AM

0 Likes
0
1685
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:34 PM . Last Modified: ‎2024-03-19 12:05 AM

It's great!

And the last...

Could you tell me about power consumption of UPS itself in operation?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:34 PM . Last Modified: ‎2024-03-19 12:05 AM

0 Likes
0
1686
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:34 PM . Last Modified: ‎2024-03-19 12:05 AM

Hi Dzung,

We have a tool call the UPS Efficieny Calculator. What it will do is tell you the UPS losses at any load. In the screenshot below, I've dropped the load down to 0 (and mind you, I am comparing the UPS to itself) and you can see it says the losses are about 185 Watts so that would be the answer to your question.

A link to this tool is here: http://www.apc.com/tool/?tt=5

8CjIwCLBOlsJtHEGUNElDA%3D%3D.jpeg8CjIwCLBOlsJtHEGUNElDA%3D%3D.jpeg

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore