Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
SUOL1000XLI New batteries not calibrated
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0101:23 AM. Last Modified: 2024-03-0601:48 AM
SUOL1000XLI New batteries not calibrated
I have an SUOL1000XLI with 1 additional battery pack cabinet. I have just replaced all three battery pack modules in it. The old ones were very run down but the UPS had been running fine for many years until recently when the charge lights had started flashing in unison.
However with the replacement batteries installed the ups charge level and run time seems not to have recalibrated properly. It indicates an expected run time of just a few minutes whereas an actual power outage test ran for nearly three hours before shut down. Running an online calibration from Power Chute made no difference either. It appears to be misjudging the degree of battery discharge, going very quickly from full charge to 2% capacity - but it will then run for a long time at that supposedly low charge level.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0101:24 AM. Last Modified: 2024-03-0601:48 AM
My problem has been resolved. I believe it was due to the load fluctuating by more than 5% during the offline manual discharge calibration. I used a 500W lamp instead of my machines and it recalibrated properly.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0101:24 AM. Last Modified: 2024-03-0601:48 AM
My problem has been resolved. I believe it was due to the load fluctuating by more than 5% during the offline manual discharge calibration. I used a 500W lamp instead of my machines and it recalibrated properly.