SUA3000 RMI 3U Internal Temperature

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUA3000 RMI 3U Internal Temperature
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:15 AM . Last Modified: ‎2024-03-12 04:37 AM

0 Likes
2
1371
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:15 AM . Last Modified: ‎2024-03-12 04:37 AM

SUA3000 RMI 3U Internal Temperature


Hi,

I have a couple of SUA3000 RMI 3U UPSs with internal temperatures running at around 45 Degrees C.

Can anyone please advise what the normal operating range should be for the internal temperature, i.e., not the ambient temperature?

regards

Dave

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 3000
  • smsrtups
  • temperature
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:15 AM . Last Modified: ‎2024-03-12 04:37 AM

0 Likes
0
1371
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:15 AM . Last Modified: ‎2024-03-12 04:37 AM

Hi Llew,

thanks a lot for the reply.

You are correct about the environmental conditions in the location, that is being looked at.

The temperature range that you see is a useful comparison, as you say, while not ideal, at least mine do not appear to be too unusual. You also make a good point about the batteries, one in particular is giving me cause for concern and I will be checking the batteries when I can get access to the UPS.

regards

Dave

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:15 AM . Last Modified: ‎2024-03-12 04:37 AM

0 Likes
0
1371
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:15 AM . Last Modified: ‎2024-03-12 04:37 AM

Hi Dave,

I don't think there is a normal operating temp for APC UPS's as the internal temperature is going to be influenced by a few environmental factors. I am not 100% sure but I do not think the UPS are designed to activate the internal fans when a certain temp is reached but rather only start operating when the UPS goes onto battery operation. Hopefully someone else on the forum can correct me. But the internal temp can be influenced by the ambient temp when the unit is in a area where there is no airflow. From the temp you have given it sounds like the unit is in this kind of environment. Another factor that could influence the internal temp is a failed battery cell so it might be a good idea to get the batteries checked to be safe. The internal temp for the units we see can range from 25 - 47ºC so while this temp is not ideal I think it is pretty normal, but I would look at the environment the unit is located and see if you can possibly make changes. If the temp is not caused by a faulty battery this temp can significantly reduce the life of your batteries.

Regards

Llew

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:15 AM . Last Modified: ‎2024-03-12 04:37 AM

0 Likes
0
1372
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:15 AM . Last Modified: ‎2024-03-12 04:37 AM

Hi Llew,

thanks a lot for the reply.

You are correct about the environmental conditions in the location, that is being looked at.

The temperature range that you see is a useful comparison, as you say, while not ideal, at least mine do not appear to be too unusual. You also make a good point about the batteries, one in particular is giving me cause for concern and I will be checking the batteries when I can get access to the UPS.

regards

Dave

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore