Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

SUA2200XL and SURTD5000RMXLP3U recharge wattage

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUA2200XL and SURTD5000RMXLP3U recharge wattage
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
sbagdon
Ensign sbagdon
Ensign

Posted: ‎2021-07-12 03:28 PM

0 Likes
3
1696
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 03:28 PM

SUA2200XL and SURTD5000RMXLP3U recharge wattage

Have a SUA2200XL  and a SURTD5000RMXLP3U... is charge wattage dependent on load?

 

For the SUA2200XL, it has a Battery Charge Power (Watts) of 271 W rated, with a rated Typical recharge time of 3 hours.

 

Will the unit charge batteries faster, the less load there is... or even powered on, no load, and exhausted batteries, it'll still take 3hrs to recharge the RBC55s? With a SUA48XLBP connected, that sounds that it'll take 9hrs to recharge.

 

Same question for the SURTD5000RMXLP3U... Battery Charge Power (Watts) of 382 W rated, with a rated Typical recharge time of 2.5hrs for the RBC140s.

 

Will that unit charge faster, with no load?

 

Thx!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX-RM
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Szabi
Ensign Szabi Ensign
Ensign

Posted: ‎2021-07-19 08:10 AM . Last Modified: ‎2021-07-19 08:16 AM

0 Likes
2
1674
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-19 08:10 AM . Last Modified: ‎2021-07-19 08:16 AM

Hi,

 

The typical recharge time for Smart-UPS is independent of load. As long as utility AC is available during the recharge cycle, the UPS units would recharge in similar timeframes whether load is connected or not. 

 

Adding external battery packs will increase the required recharge time depending on the number of RBCs in the external battery pack; as you mentioned, with an SUA48XLBP connected to the SUA2200XL, the system will require 9 hours to recharge. 

 

Let me know if you have any other questions.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

sbagdon
Ensign sbagdon
Ensign

Posted: ‎2021-07-19 10:07 AM

In response to Szabi
0 Likes
1
1668
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-19 10:07 AM

It makes sense, yet it still is unpreferable... this wold be the same with our SURTD5000RMXLP3U and SURTD5000RMXLP3U... basically, that says the onsite generator can't turn off, until the batteries are fully charged... which sounds to be from 15min to around 8-9hrs, for just about any Smart-UPS XL config. Yet just imagine if you blew a config out to 10 external packs... over 60hrs to recharge fully depleted packs... 🙂

 

Ok, so are there any configs that will charge based on load...? Is this the same, for the Symmetra line?

 

Thx!

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Szabi
Ensign Szabi Ensign
Ensign

Posted: ‎2021-07-20 01:23 AM

In response to sbagdon
0 Likes
0
1662
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-20 01:23 AM

Hi,

 

The load would not impact the battery charging rates on the Symmetra LX either.

 

If there already is a generator on site, the application could potentially be adjusted so that in case of an extended utility AC outage, the generator can power the UPS during the outage, reducing the required UPS runtime (and by extension the number of external battery packs, and the required recharge times). The UPS may still transfer to battery temporarily while the generator output is being turned on or stabilizing, but the generator would bear the brunt of the runtime.

 

Any questions, please let me know!

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore