SUA1500RMI2U On Battery Issues

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUA1500RMI2U On Battery Issues
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:56 PM . Last Modified: ‎2024-03-14 01:10 AM

0 Likes
3
1067
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:56 PM . Last Modified: ‎2024-03-14 01:10 AM

SUA1500RMI2U On Battery Issues

Hi Guys,

I need some help with my APC UPS.

I discovered this problem when there was an outage. The UPS will drop load after running on batteries for close to 5 mins.
I've checked that the UPS is accepting input, can charge the batteries to full. All indicators are normal.

My load is about 20 ~ 40% (Load indicator 2 bars), battery status is 100% (Batt level fully illuminated)

After allowing the UPS to charge for 48 Hrs. I ran a trial with the exact same load. When I unplugged the input cord, the Battery indicator will come on followed with a beep. At about 4++ mins, my loads suddently switched off. At the UPS all LEDs on the left portion (AVR Trim, Online, AVR Boost and all Load leds) will flash and there are no beeps. At the time the UPS dropped load, the batt indicator still has 4 bars.

I tried plugging the input cord back in but the UPS doesn't seemed to respond and LEDs are still flashing. I have to totally shutdown the UPS then turn it on from front panel then only it will switch to normal/charging mode. With the battery level at 4 bars I tried the entire process again and the same thing will occur after 4++ mins.

The UPS was not connected to any Powerchute clients. No serial or USB cables was used.

Need advice for this wierd case.



Regards, C.L.Chee

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:57 PM . Last Modified: ‎2024-03-14 01:10 AM

0 Likes
0
1067
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:57 PM . Last Modified: ‎2024-03-14 01:10 AM

I've managed to installed PowerChute and link via serial cable but nothing much can be seen from the event logs.

UPS Load: 52%
Line Voltage: 239V
Output: 241.9 ~ 243.3 50Hz
UPS Internal Temp: 25.6C
Battery Voltage: 27.67

When input disconnected:

Line Voltage: 0V
Output: 230.4V 50Hz
UPS Internal Temp: 26.1C
Battery Voltage: 26.86V

In the event log there's only " Power Failed" then followed by "Communication Lost" and "Communication Established" because I shutdown and restarted the UPS after it dropped load 3 minutes later.

Any Idea ?



Regards,
C.L.Chee

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:56 PM . Last Modified: ‎2024-03-14 01:10 AM

0 Likes
0
1066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:56 PM . Last Modified: ‎2024-03-14 01:10 AM

All LEDs on the left side will flash at the same time.

I've tried looking it up the manual and the closest description is that the UPS has been shut down
remotely through software but doesn't show any signs of recovery when I plugin the Input cord.

I have discovered that if I reduce the load it will be able to discharge the batteries, sleep, and then wake up and power up my computers when input resumes.

Next, I'm ganna try it out with PowerChute but I have to find the serial cable and CD first !!


Regards, C.L.Chee

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 11:57 PM . Last Modified: ‎2024-03-14 01:10 AM

0 Likes
0
1066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:57 PM . Last Modified: ‎2024-03-14 01:10 AM

hmm...sounds like that there is something wrong in the unit's circuitry. Are these lights which you mentioned flashing at the same time or alternatively? Is they any way for you to monitor the UPS through power chute to see whats going on with it?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:57 PM . Last Modified: ‎2024-03-14 01:10 AM

0 Likes
0
1068
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:57 PM . Last Modified: ‎2024-03-14 01:10 AM

I've managed to installed PowerChute and link via serial cable but nothing much can be seen from the event logs.

UPS Load: 52%
Line Voltage: 239V
Output: 241.9 ~ 243.3 50Hz
UPS Internal Temp: 25.6C
Battery Voltage: 27.67

When input disconnected:

Line Voltage: 0V
Output: 230.4V 50Hz
UPS Internal Temp: 26.1C
Battery Voltage: 26.86V

In the event log there's only " Power Failed" then followed by "Communication Lost" and "Communication Established" because I shutdown and restarted the UPS after it dropped load 3 minutes later.

Any Idea ?



Regards,
C.L.Chee

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore