SUA1500I fan noise

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUA1500I fan noise
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 11:53 PM . Last Modified: β€Ž2024-03-14 01:13 AM

0 Likes
6
1562
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:53 PM . Last Modified: β€Ž2024-03-14 01:13 AM

SUA1500I fan noise

Hi,
i'm planning to buy an APC Smart-UPS SUA1500i and I would like to know how much noise the fan do when it is operating at low speed (I saw in the kb that newer SUA1500I have a 2 speed fan, wich is always operating at low speed, and it switches at high speed only in certain conditions). I will use the ups at home (under my desk) so noise level is crucial for me.
Is it like an htpc ? like a normal pc ? like an helicopter ?

Thank you all!

Marco

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • noise_fan
  • sua1500i
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 11:53 PM . Last Modified: β€Ž2024-03-14 01:13 AM

0 Likes
0
1559
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:53 PM . Last Modified: β€Ž2024-03-14 01:13 AM

Hi all,
i bought the SUA1500I so I'm posting my impression about the noise, with the aim to leave some useful information here in the forum.
When running at low speed the fan produce a very very low amount of noise. I use the UPS near my pc (a normal pc, not an htpc or similar) and the noise of the pc hides completely the noise of the ups. When running at full speed the UPS is quite loud and you can clearly hear it (see kb 6672 to learn when the fan will operate at high speed).

In a completely silenced room you can easily ear the fan also a low speed, so i think the SUA1550I can't be positioned inside a bedroom, but it's a good choice if you can put it in a working room under the desk where you use your pc

Marco

Message was edited by: marcom76

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 11:53 PM . Last Modified: β€Ž2024-03-14 01:13 AM

0 Likes
0
1559
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:53 PM . Last Modified: β€Ž2024-03-14 01:13 AM

Here's what the [tech specs|http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SUA1500i] for this unit lists:
Audible noise at 1 meter from surface of unit: 45.00 dBA

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 11:53 PM . Last Modified: β€Ž2024-03-14 01:13 AM

0 Likes
0
1559
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:53 PM . Last Modified: β€Ž2024-03-14 01:13 AM

Hi, thank you for the link. I have already read that document, but I assume 45 db (which is a lot!) is the worst case with the fan at top speed and the ups running on battery. I would like an evaluation of the noise in normal condition, with the fan running at low speed.
Does anybody use this UPS under the desk ?

Thank you

Marco

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 11:53 PM . Last Modified: β€Ž2024-03-14 01:13 AM

0 Likes
0
1559
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:53 PM . Last Modified: β€Ž2024-03-14 01:13 AM

hi,
thank you very much for your comments. I don't think to be so sensistive to noise, and my pc haven't any ultra silent fan...it produce a "normal" noise which does not bother me. If the SUA1500I noise is similar to a "normal" pc for me could be very good.
I leave the question open, with the hope to gather more comments from other users!
Thank you

Marco

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 11:53 PM . Last Modified: β€Ž2024-03-14 01:13 AM

0 Likes
0
1559
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:53 PM . Last Modified: β€Ž2024-03-14 01:13 AM

I can't tell you anything about the SUA1500I but I was pleasantly surprised about the noise of the SUA750I. Its specs are 5dB lower than the SUA1500I and I only tried it with light loads so far but here are my observations:
-there's a fan that spins up only when operating from the battery and even then it sounds (I didn't measure it) a good bit fainter than the specs and certainly not as loud as most PCs
-there's also a faint noise under normal conditions but I don't think I could hear it from under a desk except perhaps if there were no ambient noise whatsoever (it was easily masked by the sound from the building's heating in my case so that I had to put my ear next to the unit to hear it)
Again, I didn't try heavy loads yet so, for all I know, that model makes a racket when you really load it.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 11:53 PM . Last Modified: β€Ž2024-03-14 01:13 AM

0 Likes
0
1559
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:53 PM . Last Modified: β€Ž2024-03-14 01:13 AM

Well volume is subjective... Different people have different sensitivities to sound. Personally, the noise doesn't bother me, but then again I expect to hear some noise from electrical equipment and would rather have extra noise than an overheated system. I don't go out of my way to buy the quietest fans for my computer, if that helps put it in perspective...

According to Wikipedia, 40db is like a refrigerator or library (don't quite understand that to be honest πŸ˜› ), and "the lower threshold for noise producing sleep disturbance is 45 dB(A) or lower."

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 11:53 PM . Last Modified: β€Ž2024-03-14 01:13 AM

0 Likes
0
1560
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:53 PM . Last Modified: β€Ž2024-03-14 01:13 AM

Hi all,
i bought the SUA1500I so I'm posting my impression about the noise, with the aim to leave some useful information here in the forum.
When running at low speed the fan produce a very very low amount of noise. I use the UPS near my pc (a normal pc, not an htpc or similar) and the noise of the pc hides completely the noise of the ups. When running at full speed the UPS is quite loud and you can clearly hear it (see kb 6672 to learn when the fan will operate at high speed).

In a completely silenced room you can easily ear the fan also a low speed, so i think the SUA1550I can't be positioned inside a bedroom, but it's a good choice if you can put it in a working room under the desk where you use your pc

Marco

Message was edited by: marcom76

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore