SUA1500 with new Battery

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUA1500 with new Battery
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:01 AM . Last Modified: ‎2024-03-13 11:34 PM

0 Likes
2
707
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:01 AM . Last Modified: ‎2024-03-13 11:34 PM

SUA1500 with new Battery

I just replaced the battery in my Smart UPS 1500 (SUA1500), now I'm getting the same calibration issues as lots of people have gotten here. The only thing I think I'm experiencing differently is that when I do the runtime calibration I'm not sure it's working properly.

I actually have 2 1500s, and when I perform it on one of them, it discharges properly, gets to ab out 15% then starts charging again and says successful.

The one I'm confused about is that when I do it on the other one (this is the one I just replaced the battery on), it goes to the battery for about 2 seconds, the battery charge light goes to 1 blinking LED and it goes back onto A/C. When I check the PowerChute software again, it says the battery is dischaged and does not show that the runtime calibration is still running (says it's unavailable -- due to battery not 100%).

Now I will admit, I've tried different things and can say that after I did the runtime calibration I did not allow the UPS to charge 100% before trying "something else."

So my question is, is the Powerchute runtime calibration actually doing something during this time and I should just let it go and wait for the UPS to get back up to 100% or is there another issue with the UPS that it's even failing the diagnostics.

The battery does last about 30-45 minutes with a 30% load on the battery which is normal, so I know it's just something with the calibration not the battery...I'm just not sure if it's actually doing what it should be (since it reacts differently than the other UPS).

Thanks for your help!

-Dan

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:01 AM . Last Modified: ‎2024-03-13 11:33 PM

0 Likes
0
707
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:01 AM . Last Modified: ‎2024-03-13 11:33 PM

Well it looks like after the 2nd try at the manual calibration I think it's good. What I did was hooked up 2 100w lamps, a 60w lamp and 3 80w utility lights. This made sure to give me the >30% load on the unit after 18hrs since the last charge on the battery. I drained the battery completely until it shut off, then I just plugged it in afterwards (without turning the unit on). I then got the single LED flashing as it charged. I came back about 30 minutes later to find all the lights on and the unit powered on. Again, I never turned the unit back on, it came back on by itself. I have yet to hook it up to the server to see what the powerchute says, but even with the load on it, I had 2 solid LEDs by the time I started pulling the plugged in lights off it one at a time. So I think I'm good, especially since the last time the lights flashed the entire time until it was fully charged. I'm letting it fully charge before I pull the plug and put it back on the server it's on.

Hopefully this did do it. I'm just not sure why the first time I did the manual calibration it didn't work right....!?

Oh well, hopefully I'm good now!!!

I also found out that putting distilled water into the batteries gives you good battery that lasts almost identically to any I've gotten on line (APC, ABC, or any of those)...

Now I'm collecting old batteries to keep for these two UPSes. Ha ha.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:01 AM . Last Modified: ‎2024-03-13 11:33 PM

0 Likes
0
707
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:01 AM . Last Modified: ‎2024-03-13 11:33 PM

Ohh I forgot to add to, that after about 2 or 3 minutes after I ran the runtime calibration, my PC did shut down too (gracefully as if it got sent the signal from the UPS). I thought the Powerchute software was supposed to block that so it wouldn't shut down?

Again, this was 2 or 3 minutes after the battery completely "discharged" and I'm guessing started charging back up.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:01 AM . Last Modified: ‎2024-03-13 11:33 PM

0 Likes
0
708
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:01 AM . Last Modified: ‎2024-03-13 11:33 PM

Well it looks like after the 2nd try at the manual calibration I think it's good. What I did was hooked up 2 100w lamps, a 60w lamp and 3 80w utility lights. This made sure to give me the >30% load on the unit after 18hrs since the last charge on the battery. I drained the battery completely until it shut off, then I just plugged it in afterwards (without turning the unit on). I then got the single LED flashing as it charged. I came back about 30 minutes later to find all the lights on and the unit powered on. Again, I never turned the unit back on, it came back on by itself. I have yet to hook it up to the server to see what the powerchute says, but even with the load on it, I had 2 solid LEDs by the time I started pulling the plugged in lights off it one at a time. So I think I'm good, especially since the last time the lights flashed the entire time until it was fully charged. I'm letting it fully charge before I pull the plug and put it back on the server it's on.

Hopefully this did do it. I'm just not sure why the first time I did the manual calibration it didn't work right....!?

Oh well, hopefully I'm good now!!!

I also found out that putting distilled water into the batteries gives you good battery that lasts almost identically to any I've gotten on line (APC, ABC, or any of those)...

Now I'm collecting old batteries to keep for these two UPSes. Ha ha.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of