SUA1500 shows incorrect runtime

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUA1500 shows incorrect runtime
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 01:25 AM . Last Modified: โ€Ž2024-03-13 05:36 AM

0 Likes
5
849
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 01:25 AM . Last Modified: โ€Ž2024-03-13 05:36 AM

SUA1500 shows incorrect runtime

We have about 800+ SUA1500 devices out in the field supporting each individual branch. We just replaced the battery in one of our SUA1500 devices and typically after a self test and calibration the runtimes return via the management card between 20 to 40 minutes runtime average (depends on actual load). Certain times we need to actually reset the management card for the correct runtime to be displayed.

I have a unit that no matter what we do the runtime returns to 8 minutes; even though when we run the calibration tests it will stay on battery power for 50+ minutes. What could be causing this and what can I do? I was thinking it might just be the card and was considering re-configuring a new one to send out to be replaced but if anyone has any other suggestions or if my idea is way off I really need your help.

Thank you,
Tom

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-29 01:25 AM . Last Modified: โ€Ž2024-03-13 05:36 AM

0 Likes
0
849
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 01:25 AM . Last Modified: โ€Ž2024-03-13 05:36 AM

nope ๐Ÿ™‚

i just emailed you. i am fairly confident this is the problem but we can continue via email if you'd like and let everyone know our results here.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 01:25 AM . Last Modified: โ€Ž2024-03-13 05:36 AM

0 Likes
0
849
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 01:25 AM . Last Modified: โ€Ž2024-03-13 05:36 AM

We have about 800+ SUA1500 devices out in the field supporting each individual branch. We just replaced the battery in one of our SUA1500 devices and typically after a self test and calibration the runtimes return via the management card between 20 to 40 minutes runtime average (depends on actual load). Certain times we need to actually reset the management card for the correct runtime to be displayed.

I have a unit that no matter what we do the runtime returns to 8 minutes; even though when we run the calibration tests it will stay on battery power for 50+ minutes. What could be causing this and what can I do? I was thinking it might just be the card and was considering re-configuring a new one to send out to be replaced but if anyone has any other suggestions or if my idea is way off I really need your help.

Thank you,
Tom

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-29 01:25 AM . Last Modified: โ€Ž2024-03-13 05:36 AM

0 Likes
0
849
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 01:25 AM . Last Modified: โ€Ž2024-03-13 05:36 AM

this problem is not related to the network management card. the network management card only reports what the UPS is providing it.

it sounds like you may need to do "adjust the constants."

i will PM the procedure to you if you can confirm that you can do the following:

1.) remove the NMC from the UPS
2.) obtain the APC specific serial cable - 940-0024 or 940-1524
3.) get a computer with serial port and terminal program working to interface with the UPS
4.) be comfortable using the terminal program to do this procedure - an incorrect step can possibly damage the UPS.

let me know and then I'll PM you the procedure.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 01:25 AM . Last Modified: โ€Ž2024-03-13 05:36 AM

0 Likes
0
849
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 01:25 AM . Last Modified: โ€Ž2024-03-13 05:36 AM

I can have a tech go onsite and do all of the steps you mentioned so if you could please send me the procedrues via PM that would be great! I have a few test units as well I can use to ensure the steps can be followed properly.

Thanks as I really appreciate the help

Message was edited by: TomFoolery

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 01:25 AM . Last Modified: โ€Ž2024-03-13 05:36 AM

0 Likes
0
849
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 01:25 AM . Last Modified: โ€Ž2024-03-13 05:36 AM

Email is fine...need me to PM you my email address?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-29 01:25 AM . Last Modified: โ€Ž2024-03-13 05:36 AM

0 Likes
0
850
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 01:25 AM . Last Modified: โ€Ž2024-03-13 05:36 AM

nope ๐Ÿ™‚

i just emailed you. i am fairly confident this is the problem but we can continue via email if you'd like and let everyone know our results here.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now